Relation between inside temperature, hard size cooling capacity and number of people

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result. I want to know how good the equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Relation between inside temperature, hard size cooling capacity and number of people

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result. I want to know how good the equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Relation between inside temperature, hard size cooling capacity and number of people

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result. I want to know how good the equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Relation between Effect of the number of people on the inside temperature, hard temperature (hard size cooling capacity and number of peoplecapacity)

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then
I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Effect of the number of people on the inside temperature (hard size cooling capacity)

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Effect of the number of people on the inside temperature (hard size cooling capacity)

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Effect of the number of people on the Hard sizing and inside temperature (hard size cooling capacity)temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Hard sizing AC and inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

Hard sizing AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room compared to my design condition by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I am surprised because my room is sized for 35 people. When I set 200 people, my temperature increases by barely 1deg C.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure. pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room room, compared to my design condition condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised because my with the results. My room is sized for 35 people. When people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room, compared to my design condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised with the results. My room is sized for 35 people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room, compared to my design condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised with the results. My room is sized for 35 people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room, compared to my design condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised with the results. My room is sized for 35 people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room, compared to my design condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised with the results. My room is sized for 35 people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?

AC hard sized, number of people and variation of the inside temperature

I did a auto size simulation in the purpose to find the cooling capacity of every rooms as a reference for my HVAC equipment selection. After that, I asked the supplier to give me the equipment type that match with my cooling capacity calculation result.
So I hard sized the "cooling gross total rated total capacity", "the cooling supply air flow rate" and the pressure according to the supplier's reference. Until here, no issue.
Then I want to know how good the AC equipment would be in withstanding larger number of people inside the room, compared to my design condition, by looking at the impact on my zone temperature.

I am not sure of my reasoning but I have noticed something :
- I checked and compared the "Zone sensible cooling" table, column "Calculated Design Load" with the "coil sizing summary" table, column "Coil Final Gross Sensible Capacity",
- When the "Calculated Design Load" exceeds the "Coil Final Gross Sensible Capacity", the inside temperature increase,
- When its the contrary, the temperature is equal to my set point.

I post this question because I did some tests and I am surprised with the results. My room is sized for 35 people and when I set 200 people, my temperature increases by barely 1deg C. So I am not so sure of my reasoning above.
Would it be possible for you to check whether I made good method or not, based on my objective here?