Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes: - Heating loop with electric boiler and water baseboard; - Cooling loop with electric chiller and cooling coil in HVAC loop; - Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report to:
  2. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  3. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipement exluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipement exlucing cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes: - includes:

  • Heating loop with electric boiler and water baseboard; - baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop; - loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.


The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report to:
  2. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  3. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipement exluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipement exlucing cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes:

  • Heating loop with electric boiler and water baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report Report

to:

  1. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  2. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipement exluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipement exlucing cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes:

  • Heating loop with electric boiler and water baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report

to:

  1. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  2. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipement exluding excluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipement exlucing excluding cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes:

  • Heating loop with electric boiler and water baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report

to:

  1. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  2. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipement equipment excluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipement equipment excluding cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes:

  • Heating loop with electric boiler and water baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report

to:

  1. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  2. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop) trying to compare loop)

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipment excluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipment excluding cooling coil (324 MBtu).

What can explain this disparity?

Annual cooling load VS total equipment cooling load

I'm working on a SketchUp model with OpenStudio.

The model includes:

  • Heating loop with electric boiler and water baseboard;
  • Cooling loop with electric chiller and cooling coil in HVAC loop;
  • Somes electric preheat coil, VAV reheat, electric baseboard, PTAC and DX cooling coil.

The objective is to compare the loads from:

  1. Heating (2208 MBtu) and Cooling (1001 MBtu) annual loads from HVAC Load Profiles from OpenStudio Report

to:

  1. Sum of heating equipement + Boiler load (efficiency = 1) (heating coil loop)
  2. Sum of cooling equipement + Chiller load (COP = 6.5) (Cooling coil loop)

I noted that annual heating load (2208 MBtu) equal to Boiler load (1155 MBtu) + heating equipment excluding heating coil (1054 MBtu).

The problem is for the cooling load. Annual cooling load (1001 MBtu) dot not equal to Chiller load (959 MBtu) + cooling equipment excluding cooling coil (324 MBtu).

What can explain this disparity?