I'm trying top model displacement ventilation. I'm setting the RoomAirModelType appropriately (OneNodeDisplacementVentilation, ThreeNodeDisplacementVentilation, etc.). My models has packacged single zone equipment with constant volume single zone reheat setpoint managers (supply temperature determined by cooling/heating load to setpoint). When I run I find that the HVAC system is controlling off of the Zone Air Temperature (which I believe represents the perfectly mixed condition, as opposed to the stratified condition) as opposed to the Zone Thermostat Air Temperature (which I believe correctly reflects the impact of stratification on temperature at thermostat height). The result is over-cooling in cooling mode (see plot). Is there a way to enable E+ to control to the thermostat temperature?