Hello, I am having trouble running my model. It seems to work fine when I enable ideal air loads, however when I try to run with the built HVAC system the simulation fails. There are three PTAC, one split system, and three cooling coils fed from a plant loop utilizing district heating and cooling.
Here is some of the err file
Program Version,EnergyPlus, Version 8.7.0-78a111df4a, YMD=2017.12.26 15:54,IDD_Version 8.7.0
************* IDF Context for following error/warning message:
************* Note -- lines truncated at 300 characters, if necessary...
************* 2555 Coil:Heating:Water,
************* indicated Name=VAV HW Rht Coil
************* Only last 5 lines before error line shown.....
************* 2556 VAV HW Rht Coil, !- Name
************* 2557 Always On Discrete 1, !- Availability Schedule Name
************* 2558 Autosize, !- U-Factor Times Area Value {W/K}
************* 2559 Autosize, !- Maximum Water Flow Rate {m3/s}
************* 2560 , !- Water Inlet Node Name
** Severe ** IP: IDF line~2560 Error detected in Object=COIL:HEATING:WATER, name=VAV HW RHT COIL
** ~~~ ** Field [Water Inlet Node Name] is required but was blank
************* Only last 6 lines before error line shown.....
************* 2561 , !- Water Outlet Node Name
** Severe ** IP: IDF line~8184 Error detected in Object=COIL:HEATING:WATER, name=VAV HW RHT COIL 7
** ~~~ ** Field [Water Outlet Node Name] is required but was blank
** Severe ** IP: IDF line~11579 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 2, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~11911 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 3, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~12243 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 4, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~12604 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 8, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~12916 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 7, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~13195 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 6, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~13465 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 9, Required Field=[Zone 1 Name] was blank.
************* 13629 SetpointManager:SingleZone:Reheat,
************* indicated Name=Setpoint Manager Single Zone Reheat 5
************* 13630 Setpoint Manager Single Zone Reheat 5, !- Name
************* 13631 Temperature, !- Control Variable
************* 13632 -99, !- Minimum Supply Air Temperature {C}
************* 13633 99, !- Maximum Supply Air Temperature {C}
************* 13634 , !- Control Zone Name
** Severe ** IP: IDF line~13636 Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT, name=SETPOINT MANAGER SINGLE ZONE REHEAT 5
** ~~~ ** Field [Zone Inlet Node Name] is required but was blank
** Severe ** IP: IDF line~13795 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 5, Required Field=[Zone 1 Name] was blank.
** Severe ** IP: IDF line~14140 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
** Severe ** IP: Blank "required" fields found in input
** ~~~ ** Possible Invalid Numerics or other problems
** Fatal ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=61
..... Last severe error=IP: Blank "required" fields found in input
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 61 Severe Errors; Elapsed Time=00hr 00min 0.45sec
Any help is appreciated! thanks!