I have been looking into using the Hospital Commercial/Prototype Reference Buildings to get rough ideas of energy conservation measure savings potentials. I am noticing some things that seem inaccurate, even incorrect, based on what I’m seeing in actual hospitals.
Hospital ACH-Based Air Flows
Hospital spaces related to healthcare (e.g., patient rooms, not general offices) tend to follow OA ACH and total ACH requirements established by ASHRAE Standard 170 (formerly published as AIA guidelines, currently referenced verbatim in FGI-2014). Minimum total ACH requirements can contribute heavily to fan, cooling, and reheat energy due to requiring more air than is needed for comfort conditioning and ventilation. For energy use estimation, this means that both the ACH required for the space type and space geometry need to be correct.
For an example, I will use room PatRoom2_Flr_3 as used in both the New Commercial Reference Buildings 90.1-2004 and Commercial Prototype Buildings 90.1-2013.
Ceiling (Floor-to-Floor) Height = 4.2683 m (14 ft)
Volume = 148.71 m3 (5,247.6 ft3)
Confirmed for both versions either through geometry entries or explicit definition
6 ACH has been the minimum total ACH for patient rooms for some time now (this changed recently to 4 ACH for “general” patient rooms, but that is not specifically related to this issue). Using the geometry mentioned above:
Minimum Flow - 90.1-2004 = 0.24785 m3/s = 6 ACH
Minimum Flow - 90.1-2013 = 0.007111113 m3/(s-m2) = 6 ACH
Similarly, both have 2 ACH of OA specified, the correct amount for a patient room. So far, everything looks good.
The issue is the ceiling height. I don’t have years of hospital design experience, but I've been working with ACH calculations for multiple hospitals over the past 6 months. I have yet to see any situation where there is no dropped ceiling. From what I've seen, ceiling heights tend to range from 9 ft to 10 ft for all of the space types where ASHRAE 170 is applicable. 14 ft ceiling height vs 9 ft or 10 ft can make a significant difference in OA ACH and total minimum ACH.
Other spaces in the Hospital Reference Buildings with ACH requirements appear to define airflow in the same way, using the ceiling (floor-to-floor) height, which is 14 ft in all levels except the basement.
In short, the question is:
Are all of the implementations of the Hospital Reference Building over-estimating fan, cooling, and reheat energy use due to an unrealistic representation of room volume?
(Note: My next step will be to email the contacts listed for the Reference and Prototype buildings, but I wanted to check in here first to see if I'm missing something or thinking about this wrong.)