Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV who's exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to get properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,              !- Exhaust Air Inlet Node Name <---**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors.

Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV who's exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to get properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,              !- Exhaust Air Inlet Node Name <---**THIS <--**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors. errors.

Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV who's exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,         !- Exhaust Air Inlet Node Name <--**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
Flow
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow 
Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors.

Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV who's exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow 
Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow 
Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow 
Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,        !- Exhaust Air Inlet Node Name <--**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors.

Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV who's whose exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,        !- Exhaust Air Inlet Node Name <--**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors.

Modifying ERV exhaust inlet node in OpenStudio

Hi all,

I'm working to implement an ERV whose exhaust inlet node equals an zone exhaust fan's outlet node. I'm modeling a kitchen space and hope to use this configuration to properly model heating energy savings.

In terms of the E+ model, I am able to directly modify the node (this E+ file runs successfully!):

HeatExchanger:AirToAir:SensibleAndLatent,
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow
  Node 16,                                !- Supply Air Inlet Node Name
  Node 19,                                !- Supply Air Outlet Node Name
  <EXHAUST FAN OUTLET NODE>,        !- Exhaust Air Inlet Node Name <--**THIS NODE HERE**
  Node 17,                                !- Exhaust Air Outlet Node Name
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction {dimensionless}
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

That said, OS handles these node references differently. It looks like instead of a node name, the OS HeatExchanger object references a node's outlet port (also equal to a connection's handle).

OS:HeatExchanger:AirToAir:SensibleAndLatent,
  {3cf38f75-7551-4431-8e27-85cba62e5f75}, !- Handle
  AirLoop air_handlers-204_1_BLK 1,       !- Name
  {8f9c4e1e-6e27-4b5e-b5bb-97b6c7dc597b}, !- Availability Schedule
  autosize,                               !- Nominal Supply Air Flow Rate {m3/s}
  0.45,                                   !- Sensible Effectiveness at 100% Heating Air Flow
  0,                                      !- Latent Effectiveness at 100% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 75% Heating Air Flow
  0,                                      !- Latent Effectiveness at 75% Heating Air Flow
  0.45,                                   !- Sensible Effectiveness at 100% Cooling Air Flow
  0,                                      !- Latent Effectiveness at 100% Cooling Air Flow 
  0.45,                                   !- Sensible Effectiveness at 75% Cooling Air Flow 
  0,                                      !- Latent Effectiveness at 75% Cooling Air Flow 
  {4a5780b6-1ccf-4add-9e6c-c4e4cf23e05d}, !- Supply Air Inlet Node
  {54da889f-e930-4aad-8090-0a770e88347e}, !- Supply Air Outlet Node
  {e8a8d20f-d1b6-4541-88df-449b6891f310}, !- Exhaust Air Inlet Node
  {a10c8eec-febd-4425-8b9f-e3791be3697b}, !- Exhaust Air Outlet Node
  35,                                     !- Nominal Electric Power {W}
  Yes,                                    !- Supply Air Outlet Temperature Control
  Rotary,                                 !- Heat Exchanger Type
  None,                                   !- Frost Control Type
  -30.56,                                 !- Threshold Temperature {C}
  ,                                       !- Initial Defrost Time Fraction 
  ,                                       !- Rate of Defrost Time Fraction Increase {1/K}
  Yes;                                    !- Economizer Lockout

Anyone know how best to make an equivalent change in OS? Whenever I try to manually change the OS object to reference the appropriate node's outlet ports I get errors.