Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as a Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as a an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

IDF Snippet: AirLoopHVAC:ZoneMixer, AHU-1 Return Air Mixer, !- Name AHU-1 Zone Equipment Outlet Node, !- Outlet Node Name AHU-1 Inlet Node TZ01-11, !- Inlet 1 Node Name AHU-1 Inlet Node TZ01-12, !- Inlet 2 Node Name AHU-1 Inlet Node TZ01-13, !- Inlet 3 Node Name AHU-1 Inlet Node TZ01-21, !- Inlet 4 Node Name AHU-1 Inlet Node TZ01-22, !- Inlet 5 Node Name AHU-1 Inlet Node TZ01-23, !- Inlet 6 Node Name AHU-1 Inlet Node TZ01-24, !- Inlet 7 Node Name AHU-1 Inlet Node TZ01-25, !- Inlet 8 Node Name AHU-1 Inlet Node TZ01-26, !- Inlet 9 Node Name AHU-1 Inlet Node TZ01-31; !- Inlet 10 Node Name AHU-1 Inlet Node Bypass; !- Inlet 11 Node Name

AirLoopHVAC:ZoneSplitter, AHU-1 Supply Air Splitter, !- Name AHU-1 Zone Equipment Inlet Node, !- Inlet Node Name AHU-1 Outlet Node TZ01-11, !- Outlet 1 Node Name AHU-1 Outlet Node TZ01-12, !- Outlet 2 Node Name AHU-1 Outlet Node TZ01-13, !- Outlet 3 Node Name AHU-1 Outlet Node TZ01-21, !- Outlet 4 Node Name AHU-1 Outlet Node TZ01-22, !- Outlet 5 Node Name AHU-1 Outlet Node TZ01-23, !- Outlet 6 Node Name AHU-1 Outlet Node TZ01-24, !- Outlet 7 Node Name AHU-1 Outlet Node TZ01-25, !- Outlet 8 Node Name AHU-1 Outlet Node TZ01-26, !- Outlet 9 Node Name AHU-1 Outlet Node TZ01-31, !- Outlet 10 Node Name AHU-1 Outlet Node Bypass; !- Outlet 11 Node Name

Duct, AHU Demand Bypass Duct, !- Name AHU-1 Outlet Node Bypass, !- Inlet Node Name AHU-1 Inlet Node Bypass; !- Outlet Node Name

Error Snippet *** Beginning System Sizing Calculations * Severe * Node AHU-1 OUTLET NODE BYPASS connects to no component * ~~~ * Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH * ~~~ * Check the connection to a ZoneHVAC:EquipmentConnections object * ~~~ * Check if this component is missing from the Supply Air Path * Fatal * Preceding errors cause termination

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

IDF Snippet: AirLoopHVAC:ZoneMixer, AHU-1 Return Air Mixer, !- Name AHU-1 Zone Equipment Outlet Node, !- Outlet Node Name AHU-1 Inlet Node TZ01-11, !- Inlet 1 Node Name AHU-1 Inlet Node TZ01-12, !- Inlet 2 Node Name AHU-1 Inlet Node TZ01-13, !- Inlet 3 Node Name AHU-1 Inlet Node TZ01-21, !- Inlet 4 Node Name AHU-1 Inlet Node TZ01-22, !- Inlet 5 Node Name AHU-1 Inlet Node TZ01-23, !- Inlet 6 Node Name AHU-1 Inlet Node TZ01-24, !- Inlet 7 Node Name AHU-1 Inlet Node TZ01-25, !- Inlet 8 Node Name AHU-1 Inlet Node TZ01-26, !- Inlet 9 Node Name AHU-1 Inlet Node TZ01-31; !- Inlet 10 Node Name AHU-1 Inlet Node Bypass; !- Inlet 11 Node Name

AirLoopHVAC:ZoneSplitter, AHU-1 Supply Air Splitter, !- Name AHU-1 Zone Equipment Inlet Node, !- Inlet Node Name AHU-1 Outlet Node TZ01-11, !- Outlet 1 Node Name AHU-1 Outlet Node TZ01-12, !- Outlet 2 Node Name AHU-1 Outlet Node TZ01-13, !- Outlet 3 Node Name AHU-1 Outlet Node TZ01-21, !- Outlet 4 Node Name AHU-1 Outlet Node TZ01-22, !- Outlet 5 Node Name AHU-1 Outlet Node TZ01-23, !- Outlet 6 Node Name AHU-1 Outlet Node TZ01-24, !- Outlet 7 Node Name AHU-1 Outlet Node TZ01-25, !- Outlet 8 Node Name AHU-1 Outlet Node TZ01-26, !- Outlet 9 Node Name AHU-1 Outlet Node TZ01-31, !- Outlet 10 Node Name AHU-1 Outlet Node Bypass; !- Outlet 11 Node Name

Duct, AHU Demand Bypass Duct, !- Name AHU-1 Outlet Node Bypass, !- Inlet Node Name AHU-1 Inlet Node Bypass; !- Outlet Node Name

Error Snippet ***

************* Beginning System Sizing Calculations
 

* Severe * Node AHU-1 OUTLET NODE BYPASS connects to no component * ~~~ * Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH * ~~~ * Check the connection to a ZoneHVAC:EquipmentConnections object * ~~~ * Check if this component is missing from the Supply Air Path * Fatal * Preceding errors cause termination

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

AirLoopHVAC:ZoneMixer, AHU-1 Return Air Mixer, !- Name AHU-1 Zone Equipment Outlet Node, !- Outlet Node Name AHU-1 Inlet Node TZ01-11, !- Inlet 1 Node Name AHU-1 Inlet Node TZ01-12, !- Inlet 2 Node Name AHU-1 Inlet Node TZ01-13, !- Inlet 3 Node Name AHU-1 Inlet Node TZ01-21, !- Inlet 4 Node Name AHU-1 Inlet Node TZ01-22, !- Inlet 5 Node Name AHU-1 Inlet Node TZ01-23, !- Inlet 6 Node Name AHU-1 Inlet Node TZ01-24, !- Inlet 7 Node Name AHU-1 Inlet Node TZ01-25, !- Inlet 8 Node Name AHU-1 Inlet Node TZ01-26, !- Inlet 9 Node Name AHU-1 Inlet Node TZ01-31; !- Inlet 10 Node Name AHU-1 Inlet Node Bypass; !- Inlet 11 Node Name

AirLoopHVAC:ZoneSplitter, AHU-1 Supply Air Splitter, !- Name AHU-1 Zone Equipment Inlet Node, !- Inlet Node Name AHU-1 Outlet Node TZ01-11, !- Outlet 1 Node Name AHU-1 Outlet Node TZ01-12, !- Outlet 2 Node Name AHU-1 Outlet Node TZ01-13, !- Outlet 3 Node Name AHU-1 Outlet Node TZ01-21, !- Outlet 4 Node Name AHU-1 Outlet Node TZ01-22, !- Outlet 5 Node Name AHU-1 Outlet Node TZ01-23, !- Outlet 6 Node Name AHU-1 Outlet Node TZ01-24, !- Outlet 7 Node Name AHU-1 Outlet Node TZ01-25, !- Outlet 8 Node Name AHU-1 Outlet Node TZ01-26, !- Outlet 9 Node Name AHU-1 Outlet Node TZ01-31, !- Outlet 10 Node Name AHU-1 Outlet Node Bypass; !- Outlet 11 Node Name

Duct, AHU Demand Bypass Duct, !- Name AHU-1 Outlet Node Bypass, !- Inlet Node Name AHU-1 Inlet Node Bypass; !- Outlet Node Name

************* Beginning System Sizing Calculations

* Severe * Node AHU-1 OUTLET NODE BYPASS connects to no component * ~~~ * Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH * ~~~ * Check the connection to a ZoneHVAC:EquipmentConnections object * ~~~ * Check if this component is missing from the Supply Air Path * Fatal * Preceding errors cause termination

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

AirLoopHVAC:ZoneMixer,
  AHU-1 Return Air Mixer,            !- Name
  AHU-1 Zone Equipment Outlet Node,  !- Outlet Node Name
  AHU-1 Inlet Node TZ01-11,          !- Inlet 1 Node Name
  AHU-1 Inlet Node TZ01-12,          !- Inlet 2 Node Name
  AHU-1 Inlet Node TZ01-13,          !- Inlet 3 Node Name
  AHU-1 Inlet Node TZ01-21,          !- Inlet 4 Node Name
  AHU-1 Inlet Node TZ01-22,          !- Inlet 5 Node Name
  AHU-1 Inlet Node TZ01-23,          !- Inlet 6 Node Name
  AHU-1 Inlet Node TZ01-24,          !- Inlet 7 Node Name
  AHU-1 Inlet Node TZ01-25,          !- Inlet 8 Node Name
  AHU-1 Inlet Node TZ01-26,          !- Inlet 9 Node Name
  AHU-1 Inlet Node TZ01-31;          !- Inlet 10 Node Name
  AHU-1 Inlet Node Bypass;           !- Inlet 11 Node Name

Name AirLoopHVAC:ZoneSplitter, AHU-1 Supply Air Splitter, !- Name AHU-1 Zone Equipment Inlet Node, !- Inlet Node Name AHU-1 Outlet Node TZ01-11, !- Outlet 1 Node Name AHU-1 Outlet Node TZ01-12, !- Outlet 2 Node Name AHU-1 Outlet Node TZ01-13, !- Outlet 3 Node Name AHU-1 Outlet Node TZ01-21, !- Outlet 4 Node Name AHU-1 Outlet Node TZ01-22, !- Outlet 5 Node Name AHU-1 Outlet Node TZ01-23, !- Outlet 6 Node Name AHU-1 Outlet Node TZ01-24, !- Outlet 7 Node Name AHU-1 Outlet Node TZ01-25, !- Outlet 8 Node Name AHU-1 Outlet Node TZ01-26, !- Outlet 9 Node Name AHU-1 Outlet Node TZ01-31, !- Outlet 10 Node Name AHU-1 Outlet Node Bypass; !- Outlet 11 Node Name

Name Duct, AHU Demand Bypass Duct, !- Name AHU-1 Outlet Node Bypass, !- Inlet Node Name AHU-1 Inlet Node Bypass; !- Outlet Node Name

Name

************* Beginning System Sizing Calculations

* ** Severe * ** Node AHU-1 OUTLET NODE BYPASS connects to no component * ** ~~~ * ** Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH * ** ~~~ * ** Check the connection to a ZoneHVAC:EquipmentConnections object * ** ~~~ * ** Check if this component is missing from the Supply Air Path * ** Fatal * ** Preceding errors cause terminationtermination

Thanks

Can the Duct E+ object be used to make a AirLoop demand-side bypass?

How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.

AirLoopHVAC:ZoneMixer,
  AHU-1 Return Air Mixer,            !- Name
  AHU-1 Zone Equipment Outlet Node,  !- Outlet Node Name
  AHU-1 Inlet Node TZ01-11,          !- Inlet 1 Node Name
  AHU-1 Inlet Node TZ01-12,          !- Inlet 2 Node Name
  AHU-1 Inlet Node TZ01-13,          !- Inlet 3 Node Name
  AHU-1 Inlet Node TZ01-21,          !- Inlet 4 Node Name
  AHU-1 Inlet Node TZ01-22,          !- Inlet 5 Node Name
  AHU-1 Inlet Node TZ01-23,          !- Inlet 6 Node Name
  AHU-1 Inlet Node TZ01-24,          !- Inlet 7 Node Name
  AHU-1 Inlet Node TZ01-25,          !- Inlet 8 Node Name
  AHU-1 Inlet Node TZ01-26,          !- Inlet 9 Node Name
  AHU-1 Inlet Node TZ01-31;          !- Inlet 10 Node Name
  AHU-1 Inlet Node Bypass;           !- Inlet 11 Node Name

AirLoopHVAC:ZoneSplitter,
  AHU-1 Supply Air Splitter,        !- Name
  AHU-1 Zone Equipment Inlet Node,  !- Inlet Node Name
  AHU-1 Outlet Node TZ01-11,        !- Outlet 1 Node Name
  AHU-1 Outlet Node TZ01-12,        !- Outlet 2 Node Name
  AHU-1 Outlet Node TZ01-13,        !- Outlet 3 Node Name
  AHU-1 Outlet Node TZ01-21,        !- Outlet 4 Node Name
  AHU-1 Outlet Node TZ01-22,        !- Outlet 5 Node Name
  AHU-1 Outlet Node TZ01-23,        !- Outlet 6 Node Name
  AHU-1 Outlet Node TZ01-24,        !- Outlet 7 Node Name
  AHU-1 Outlet Node TZ01-25,        !- Outlet 8 Node Name
  AHU-1 Outlet Node TZ01-26,        !- Outlet 9 Node Name
  AHU-1 Outlet Node TZ01-31,        !- Outlet 10 Node Name
  AHU-1 Outlet Node Bypass;         !- Outlet 11 Node Name

Duct,
  AHU Demand Bypass Duct,   !- Name
  AHU-1 Outlet Node Bypass, !- Inlet Node Name
  AHU-1 Inlet Node Bypass;  !- Outlet Node Name

************* Beginning System Sizing Calculations
** Severe  ** Node AHU-1 OUTLET NODE BYPASS connects to no component
**   ~~~   ** Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH
**   ~~~   ** Check the connection to a ZoneHVAC:EquipmentConnections object
**   ~~~   ** Check if this component is missing from the Supply Air Path
**  Fatal  ** Preceding errors cause termination

Thanks