62.1 VRP Heating Min Zone Primary Airflow
I'm using the ASHRAE 62.1 ventilation rate procedure in OpenStuido v1.14, and am having difficulty finding the input to increase the minimum zone primary airflow for heating (Vpz-min), so that my critical zone Zpz is lower. I am using a basic VAV reheat system with AirTerminal:SingleDuct:VAV:Reheat.
I am having a similar issue to this question but with a standard VAV system. And the suggestion to decrease reheat supply air temperature has not yielded results. I am very familiar with ASRHAE 62.1 spreadsheet calculations, and believe that I know what the issue is but can't get the values to change.
The design size max air flow rate is 2781 cfm. The design size minimum air flow rate is 834 cfm (based on a zone minimum air flow input method of "constant" at 30%).
The design size reheat coil sizing air volume flow rate is 1226 cfm. This is the same as the minimum zone primary airflow for heating. However, I can't figure out how to increase this value. Increasing the zone minimum air flow input to 50% raises the design size reheat coil sizing air volume flow rate to 1390 cfm, but the minimum zone primary airflow for heating won't budge. Its still at 1226 cfm (lower than the reheat coil air volume flow rate)
Any suggestions would be appreciated.