Fan power calculation for variable speed Fan:OnOff

I am modeling a multispeed coil (Coil:Cooling:DX:Multispeed) and a variable speed fan using the Fan:OnOff object (I want it to be able to cycle). According to the documentation, if you wish to model a variable speed fan you need to provide a fan curve that represents the ratio of actual fan power to rated fan power when a change in fan speed occurs. If my understanding of the documentation is correct, for example, if my rated fan power is 1000W and that my fan is running at a PLR of 0.6 and that my curve returns a value of 0.4 my actual fan power should be 400W. I tried with several different curves but I couldn’t get my fan power to be calculated according to my interpretation.

To get a better understanding of what EnergyPlus is doing, I took a quick peek at the source code. I noticed that on line 1926 through 1930 there is an if/else statement that sets the fan run time fraction equals to the part load ratio if “OnOffFanPartLoadFraction” is equal to 1. In the case where my fan’s “OnOffFanPartLoadFRaction” is 1 but is running at a PLR < 1, then the fan runtime fraction used in the fan power calculation is going to be equal to my PLR and used as is in the fan power calculation. I ran hourly reports and for all hours where my fan PLR was < 1 but the fan RTF = 1, I divided the fan power calculated by EnergyPlus by the hourly PLR and got the fan power I was expecting to get, which for the previous example (rated fan power 1000W, at a PLR of 0.6 output of the curve 0.4) EnergyPlus is returning a fan power = 1000 * 0.6 * 0.4, whereas if my understanding of the documentation is correct it should return 1000 * 0.4.

To get what I wanted, I created a new curve based on the regression of the output of my original curve divided by the PLR as a function of the PLR. However, I am still curious to know what is going on, if I am just not interpreting the documentation properly or if there is something going on with the code or if something else in my model could be causing this behavior.

Fan power calculation for variable speed Fan:OnOff

I am modeling a multispeed coil (Coil:Cooling:DX:Multispeed) and a variable speed fan using the Fan:OnOff object (I want it to be able to cycle). According to the documentation, if you wish to model a variable speed fan you need to provide a fan curve that represents the ratio of actual fan power to rated fan power when a change in fan speed occurs. If my understanding of the documentation is correct, for example, if my rated fan power is 1000W and that my fan is running at a PLR of 0.6 and that my curve returns a value of 0.4 my actual fan power should be 400W. I tried with several different curves but I couldn’t get my fan power to be calculated according to my interpretation.

To get a better understanding of what EnergyPlus is doing, I took a quick peek at the source code. I noticed that on line 1926 through 1930 there is an if/else statement that sets the fan run time fraction equals to the part load ratio if “OnOffFanPartLoadFraction” is equal to 1. In the case where my fan’s “OnOffFanPartLoadFRaction” is 1 but is running at a PLR < 1, then the fan runtime fraction used in the fan power calculation is going to be equal to my PLR and used as is in the fan power calculation. I ran hourly reports and for all hours where my fan PLR was < 1 but the fan RTF = 1, I divided the fan power calculated by EnergyPlus by the hourly PLR and got the fan power I was expecting to get, which for the previous example (rated fan power 1000W, at a PLR of 0.6 output of the curve 0.4) EnergyPlus is returning a fan power = 1000 * 0.6 * 0.4, whereas if my understanding of the documentation is correct it should return 1000 * 0.4.

To get what I wanted, I created a new curve based on the regression of the output of my original curve divided by the PLR as a function of the PLR. However, I am still curious to know what is going on, if I am just not interpreting the documentation properly or if there is something going on with the code or if something else in my model could be causing this behavior.behavior. __

EDIT:

@rraustad: Thank you for providing an explanation of the code. Perhaps my question was not well written because I’m not sure you understood what I am trying to do. In short, I would like the fan power to be calculated using a fan power modifier that is function of the fan part load ratio. In DOE-2, this can be done using the FAN-EIR-FPLR keyword which is defined as follows:

FAN-EIR-FPLR is a “curve that gives the ratio of fan electric energy to full-load fan electric energy, as a function of part-load ratio […]”

In my EnergyPlus model I have to use a Fan:OnOff object since I want my fan to be able to cycle. According to the documentation the Fan:OnOff object can be used with variable speed systems. In order to model a variable speed fan I need to provide a “Fan Power Ratio Function of Speed Ratio Curve”. This curve is defined in the documentation as follows:

Fan Power Ratio Function of Speed Ratio Curve “represents the ratio of actual fan power to rated fan power when a change in fan speed occurs.”

To me, this definition is identical to the FAN-EIR-FPLR since according to the affinity laws, fan speed and airflow are proportional.

I would like to model the following fan power modifier curve in EnergyPlus: $\frac{P_{fan}}{P_{rated}} = 1.7647 (PLR) – 0.7647$, with a minimum output of 0.4. I used this curve (exponential version of it) in EnergyPlus and noticed that the calculated fan power was always lower than expected. Here’s an example:

image description

The rated fan power in this example is ~1.309 kW, the PLR on the 5/4 at 3pm is 0.66, the output of the curve should be 0.40 and so the fan power calculated by EnergyPlus should be 1.309 * 0.4 = ~0.53 kW however, as the example shows, the fan power calculated by energy plus is 0.35 kW.

I tried several different curves but the fan power calculated by EnergyPlus was never what I was expecting it to be. I decided to use a constant curve to try to see if I could find a relationship between the fan PLR and the calculated fan power. I noticed that the output of the curve was somehow multiplied by the fan PLR in the fan power calculation. Here’s an example:

image description

The rated fan power is ~1.309 kW, the PLR on the 5/4 at 3pm is 0.68, the output of the curve is 1 so the actual fan power should be the same as the rated fan power. However, it is equal to the rated fan power multiplied by the PLR: 1.309 * 0.68 = 0.89 kW.

Upon noticing that, I created a new curve based on a regression of the output of the original curve divided by the PLR as a function of the PLR. Doing so helped me obtain the expected fan power in Energy Plus. Here’s an example:

  • Original curve: $\frac{P_{fan}}{P_{fan_rated}} = 1.7647 (PLR) – 0.7647$
  • New curve: $\frac{P_{fan}}{P_{fan_rated}} = 1.1587 (PLR) – 0.1405$

image description

On the 5/4 at 3pm, the fan PLR is 0.67 which gives a rated fan power modifier of 0.4 according to the original curve which results in a fan power of 1.309 * 0.42 =~ 0.55 kW.

Additionally, if we look back at the first example and take the expected fan power (~0.53kW) and multiply it by the PLR (0.66) we get what EnergyPlus calculated, ~ 0.35kW.

I created this post in hopes of learning why I wasn’t getting the results that I was initially expecting. I am not sure how the affinity laws would play a role here. In DOE-2, the user can use any FAN-EIR-FPLR curve no matter how crazy or wrong it is, the power will be calculated according to the output of the curve.

Even if my “work-around” seems to give me the answer that I am expecting, I am still curious to know why I had to go this route or if I am missing something somewhere along the way.

Fan power calculation for variable speed Fan:OnOff

I am modeling a multispeed coil (Coil:Cooling:DX:Multispeed) and a variable speed fan using the Fan:OnOff object (I want it to be able to cycle). According to the documentation, if you wish to model a variable speed fan you need to provide a fan curve that represents the ratio of actual fan power to rated fan power when a change in fan speed occurs. If my understanding of the documentation is correct, for example, if my rated fan power is 1000W and that my fan is running at a PLR of 0.6 and that my curve returns a value of 0.4 my actual fan power should be 400W. I tried with several different curves but I couldn’t get my fan power to be calculated according to my interpretation.

To get a better understanding of what EnergyPlus is doing, I took a quick peek at the source code. I noticed that on line 1926 through 1930 there is an if/else statement that sets the fan run time fraction equals to the part load ratio if “OnOffFanPartLoadFraction” is equal to 1. In the case where my fan’s “OnOffFanPartLoadFRaction” is 1 but is running at a PLR < 1, then the fan runtime fraction used in the fan power calculation is going to be equal to my PLR and used as is in the fan power calculation. I ran hourly reports and for all hours where my fan PLR was < 1 but the fan RTF = 1, I divided the fan power calculated by EnergyPlus by the hourly PLR and got the fan power I was expecting to get, which for the previous example (rated fan power 1000W, at a PLR of 0.6 output of the curve 0.4) EnergyPlus is returning a fan power = 1000 * 0.6 * 0.4, whereas if my understanding of the documentation is correct it should return 1000 * 0.4.

To get what I wanted, I created a new curve based on the regression of the output of my original curve divided by the PLR as a function of the PLR. However, I am still curious to know what is going on, if I am just not interpreting the documentation properly or if there is something going on with the code or if something else in my model could be causing this behavior. __behavior.

EDIT:

@rraustad: Thank you for providing an explanation of the code. Perhaps my question was not well written because I’m not sure you understood what I am trying to do. In short, I would like the fan power to be calculated using a fan power modifier that is function of the fan part load ratio. In DOE-2, this can be done using the FAN-EIR-FPLR keyword which is defined as follows:

FAN-EIR-FPLR is a “curve that gives the ratio of fan electric energy to full-load fan electric energy, as a function of part-load ratio […]”

In my EnergyPlus model I have to use a Fan:OnOff object since I want my fan to be able to cycle. According to the documentation the Fan:OnOff object can be used with variable speed systems. In order to model a variable speed fan I need to provide a “Fan Power Ratio Function of Speed Ratio Curve”. This curve is defined in the documentation as follows:

Fan Power Ratio Function of Speed Ratio Curve “represents the ratio of actual fan power to rated fan power when a change in fan speed occurs.”

To me, this definition is identical to the FAN-EIR-FPLR since according to the affinity laws, fan speed and airflow are proportional.

I would like to model the following fan power modifier curve in EnergyPlus: $\frac{P_{fan}}{P_{rated}} = 1.7647 (PLR) – 0.7647$, with a minimum output of 0.4. I used this curve (exponential version of it) in EnergyPlus and noticed that the calculated fan power was always lower than expected. Here’s an example:

image description

The rated fan power in this example is ~1.309 kW, the PLR on the 5/4 at 3pm is 0.66, the output of the curve should be 0.40 and so the fan power calculated by EnergyPlus should be 1.309 * 0.4 = ~0.53 kW however, as the example shows, the fan power calculated by energy plus is 0.35 kW.

I tried several different curves but the fan power calculated by EnergyPlus was never what I was expecting it to be. I decided to use a constant curve to try to see if I could find a relationship between the fan PLR and the calculated fan power. I noticed that the output of the curve was somehow multiplied by the fan PLR in the fan power calculation. Here’s an example:

image description

The rated fan power is ~1.309 kW, the PLR on the 5/4 at 3pm is 0.68, the output of the curve is 1 so the actual fan power should be the same as the rated fan power. However, it is equal to the rated fan power multiplied by the PLR: 1.309 * 0.68 = 0.89 kW.

Upon noticing that, I created a new curve based on a regression of the output of the original curve divided by the PLR as a function of the PLR. Doing so helped me obtain the expected fan power in Energy Plus. Here’s an example:

  • Original curve: $\frac{P_{fan}}{P_{fan_rated}} = 1.7647 (PLR) – 0.7647$
  • New curve: $\frac{P_{fan}}{P_{fan_rated}} = 1.1587 (PLR) – 0.1405$

image description

On the 5/4 at 3pm, the fan PLR is 0.67 which gives a rated fan power modifier of 0.4 according to the original curve which results in a fan power of 1.309 * 0.42 =~ 0.55 kW.

Additionally, if we look back at the first example and take the expected fan power (~0.53kW) and multiply it by the PLR (0.66) we get what EnergyPlus calculated, ~ 0.35kW.

I created this post in hopes of learning why I wasn’t getting the results that I was initially expecting. I am not sure how the affinity laws would play a role here. In DOE-2, the user can use any FAN-EIR-FPLR curve no matter how crazy or wrong it is, the power will be calculated according to the output of the curve.

Even if my “work-around” seems to give me the answer that I am expecting, I am still curious to know why I had to go this route or if I am missing something somewhere along the way.