Outdoor Air Summary Report is 40% of the Outdoor Air setted?

Why Outdoor Air Flow in the Outdoor Air Summary Report is always 40% of the Outdoor Air setted?

I have a model with system Package Rooftop and the Outdoor Air System is setted for a minimmum and a maximmum of 153 cfm. Althought, when I calculate the flow in the Outdoor Air Summary Report (ACH x Zone Volume / 60), this is often as 40% of I had setted in the Outdoor Air System.

image description

image description

Outdoor Air Summary Report is 40% of the Outdoor Air setted?

Why Outdoor Air Flow in the Outdoor Air Summary Report is always 40% of the Outdoor Air setted?

I have a model with system Package Rooftop and the Outdoor Air System is setted for a minimmum minimum and a maximmum maximum of 153 cfm. Althought, when I calculate the flow in the Outdoor Air Summary Report (ACH x Zone Volume / 60), this is often as 40% 63 cfm (40%) of I had setted in the Outdoor Air System. This occur in all systems of the model.

image description

image description

Outdoor Air Summary Report is 40% of the Outdoor Air setted?

Why Outdoor Air Flow in the Outdoor Air Summary Report is always 40% of the Outdoor Air setted?

I have a model with system Package Rooftop and the Outdoor Air System is setted for a minimum and a maximum of 153 cfm. Althought, when I calculate the flow in the Outdoor Air Summary Report (ACH x Zone Volume / 60), this is 63 cfm (40%) of I had setted in the Outdoor Air System. This occur in all systems of the model.

image description

image description

image description

Outdoor Air Summary Report is 40% of the Outdoor Air setted?

Why Outdoor Air Flow in the Outdoor Air Summary Report is always 40% of the Outdoor Air setted?

I have a model with system Package Rooftop and the Outdoor Air System is setted for a minimum and a maximum of 153 cfm. Althought, when I calculate the flow in the Outdoor Air Summary Report (ACH x Zone Volume / 60), this is 63 cfm (40%) of I had setted in the Outdoor Air System. This occur in all systems of the model.

image description

image description

image description

image description

Outdoor Air Summary Report is 40% of the Outdoor Air setted?

Why Outdoor Air Flow in the Outdoor Air Summary Report is always 40% of the Outdoor Air setted?

I have a model with system Package Rooftop and the Outdoor Air System is setted for a minimum and a maximum of 153 cfm. Althought, when I calculate the flow in the Outdoor Air Summary Report (ACH x Zone Volume / 60), this is 63 cfm (40%) of I had setted in the Outdoor Air System. This occur in all systems of the model.

image description

image description

image description

image description