HArdsizing outdoor air in HVAC: When multiple input fields are given, which one takes precedence?

I am trying to hardsize the outdoor air requirements for my models in Openstudio 1.12.0, and I'm having problems in getting the systems to use the value of the outdoor air I have given as an input
I'm running two models: - Model 1 (baseline) has VAV systems serving on OS:AirLoopHVAC loops serving the corridor zones , ZoneHVAC:PackagedTerminalHeatPump serving apartment zones and ZoneHVACPackagedTerminalAirConditioners serving office and exercise zones. - Model 2(Proposed) has ZoneHVACPackagedTerminalAirConditioners serving apartments, Make up air units serving corridor zones, and furnaces serving the eercise and office zones.

I want to specify the outdoor airflow rate for all these systems. With regard to this, for the Make up air units, as per the answer provided for [https://unmethours.com/question/10181/mau-airflow-night-setback/] , the outdoor air provided in "OS:DesignSpecificationOutdoorAir" for the spacetypes of the zones overrides the the value entered in the MinimumOutdoorAirFlowRate in OS:ControllerOutdoorAir and DesignOutdoorAirFlowRate in OS:Sizing:System.

However, OS:DesignSpecificationOutdoorAir does not override values of outdoor air I enter in "outdoor-air-flow-rate-when-no-cooling-or-heating-is-needed" under OS:PackagedTerminalAirConditioner or in ZoneHVAC:PackagedTerminalHeatPump. The values entered in DesignOutdoorAirFlowRate in OS:AirLoopHVAC and MinimumOutdoorAirFlowRate in OS:AirLoopHVAC:OutdoorAirSystem also override the DesignSpecificationOutdoorAir value.

Is this always the case? Does anyone know of a clear heirarchy of which entry overrides the other, specifically for each of these systems? (PTAC,PTHP, VAV and Makup air units). Why is this level of precedence different only for a make up air unit when compared to other systems? I am not able to find any documentation which says one clearly overrides the other, and the modelling suggests that this may be system specific. Can someone clarify?

Also, when I check the energyplus output files for a system, say, ZoneHVAC:PackagedTerminalHeatPump, there are two values of outside air: the User-Specified Outdoor Air Flow Rate and the Design Size Outdoor Air Flow Rate. How is this design size outdoor airflow rate value calculated? Does it use the inputs from DesignSpecificationOutdoorAir?

HArdsizing outdoor air in HVAC: When multiple input fields are given, which one takes precedence?

I am trying to hardsize the outdoor air requirements for my models in Openstudio 1.12.0, and I'm having problems in getting the systems to use the value of the outdoor air I have given as an input
I'm running two models: - Model 1 (baseline) has VAV systems serving on OS:AirLoopHVAC loops serving the corridor zones , ZoneHVAC:PackagedTerminalHeatPump serving apartment zones and ZoneHVACPackagedTerminalAirConditioners serving office and exercise zones. - Model 2(Proposed) has ZoneHVACPackagedTerminalAirConditioners serving apartments, Make up air units serving corridor zones, and furnaces serving the eercise and office zones.

I want to specify the outdoor airflow rate for all these systems. With regard to this, for the Make up air units, as per the answer provided for [https://unmethours.com/question/10181/mau-airflow-night-setback/] , the outdoor air provided in "OS:DesignSpecificationOutdoorAir" for the spacetypes of the zones overrides the the value entered in the MinimumOutdoorAirFlowRate in OS:ControllerOutdoorAir and DesignOutdoorAirFlowRate in OS:Sizing:System.

However, OS:DesignSpecificationOutdoorAir does not override values of outdoor air I enter in "outdoor-air-flow-rate-when-no-cooling-or-heating-is-needed" under OS:PackagedTerminalAirConditioner or in ZoneHVAC:PackagedTerminalHeatPump. The values entered in DesignOutdoorAirFlowRate in OS:AirLoopHVAC and MinimumOutdoorAirFlowRate in OS:AirLoopHVAC:OutdoorAirSystem also override the DesignSpecificationOutdoorAir value.

Is this always the case? Does anyone know of a clear heirarchy of which entry overrides the other, specifically for each of these systems? (PTAC,PTHP, VAV and Makup air units). Why is this level of precedence different only for a make up air unit when compared to other systems? I am not able to find any documentation which says one clearly overrides the other, and the modelling suggests that this may be system specific. Can someone clarify?

Also, when I check the energyplus output files for a system, say, ZoneHVAC:PackagedTerminalHeatPump, there are two values of outside air: the User-Specified Outdoor Air Flow Rate and the Design Size Outdoor Air Flow Rate. How is this design size outdoor airflow rate value calculated? Does it use the inputs from DesignSpecificationOutdoorAir?

HArdsizing outdoor air in HVAC: When multiple input fields are given, which one takes precedence?

I am trying to hardsize the outdoor air requirements for my models in Openstudio 1.12.0, and I'm having problems in getting the systems to use the value of the outdoor air I have given as an input
I'm running two models: - Model 1 (baseline) has VAV systems serving on OS:AirLoopHVAC loops serving the corridor zones , ZoneHVAC:PackagedTerminalHeatPump serving apartment zones and ZoneHVACPackagedTerminalAirConditioners serving office and exercise zones. - Model 2(Proposed) has ZoneHVACPackagedTerminalAirConditioners serving apartments, Make up air units serving corridor zones, and furnaces serving the eercise and office zones.

I want to specify the outdoor airflow rate for all these systems. With regard to this, for the Make up air units, as per the answer provided for [https://unmethours.com/question/10181/mau-airflow-night-setback/] , the outdoor air provided in "OS:DesignSpecificationOutdoorAir" for the spacetypes of the zones overrides the the value entered in the MinimumOutdoorAirFlowRate in OS:ControllerOutdoorAir and DesignOutdoorAirFlowRate in OS:Sizing:System.

However, OS:DesignSpecificationOutdoorAir does not override values of outdoor air I enter in "outdoor-air-flow-rate-when-no-cooling-or-heating-is-needed" under OS:PackagedTerminalAirConditioner or in ZoneHVAC:PackagedTerminalHeatPump. The values entered in DesignOutdoorAirFlowRate in OS:AirLoopHVAC and MinimumOutdoorAirFlowRate in OS:AirLoopHVAC:OutdoorAirSystem also override the DesignSpecificationOutdoorAir value.

Is this always the case? Does anyone know of a clear heirarchy of which entry overrides the other, specifically for each of these systems? (PTAC,PTHP, VAV and Makup air units). Why is this level of precedence different only for a make up air unit when compared to other systems? I am not able to find any documentation which says one clearly overrides the other, and the modelling suggests that this may be system specific. Can someone clarify?

Also, when I check the energyplus output files for a system, say, ZoneHVAC:PackagedTerminalHeatPump, there are two values of outside air: the User-Specified Outdoor Air Flow Rate and the Design Size Outdoor Air Flow Rate. How is this design size outdoor airflow rate value calculated? Does it use the inputs from DesignSpecificationOutdoorAir?