Chiller selection/modification for Ice storage

I am using the chillers provided by default for the CHILLER:ELECTRIC:REFORMULATEDEIR as

Bicubic:ReformEIRChiller Carrier 19XR 1259kW/6.26COP/Vanes EIRFPLR,

ReformEIRChiller Carrier 19XR 1259kW/6.26COP/Vanes EIRFPLR,  !- Name
4.602131E-02,            !- Coefficient1 Constant
2.433945E-02,            !- Coefficient2 x
6.394526E-05,            !- Coefficient3 x**2
-3.648563E-01,           !- Coefficient4 y
1.854759E+00,            !- Coefficient5 y**2
-2.809346E-02,           !- Coefficient6 x*y
0.000000E+00,            !- Coefficient7 x**3
-4.821515E-01,           !- Coefficient8 y**3
0.000000E+00,            !- Coefficient9 x**2*y
0.000000E+00,            !- Coefficient10 x*y**2
14.56,                   !- Minimum Value of x
34.97,                   !- Maximum Value of x
0.18,                    !- Minimum Value of y
1.03,                    !- Maximum Value of y
,                        !- Minimum Curve Output
,                        !- Maximum Curve Output
Temperature,             !- Input Unit Type for X
Dimensionless,           !- Input Unit Type for Y
Dimensionless;           !- Output Unit Type

Biquadratic:WC Screw Default 90.1-2004 Cap_fT

Curve:Biquadratic,
WC Screw Default 90.1-2004 Cap_fT,  !- Name
0.9061150,               !- Coefficient1 Constant
0.0292277,               !- Coefficient2 x
-0.0003647,              !- Coefficient3 x**2
-0.0009709,              !- Coefficient4 y
-0.0000905,              !- Coefficient5 y**2
0.0002527,               !- Coefficient6 x*y
0.0,                     !- Minimum Value of x
20.0,                    !- Maximum Value of x
0.0,                     !- Minimum Value of y
50.0;                    !- Maximum Value of y

Biquadratic:WC Screw Default 90.1-2004 EIR_fT

Curve:Biquadratic,
WC Screw Default 90.1-2004 EIR_fT,  !- Name
0.3617105,               !- Coefficient1 Constant
-0.0229833,              !- Coefficient2 x
-0.0009519,              !- Coefficient3 x**2
0.0131889,               !- Coefficient4 y
0.0003752,               !- Coefficient5 y**2
-0.0007059,              !- Coefficient6 x*y
0.0,                     !- Minimum Value of x
20.0,                    !- Maximum Value of x
0.0,                     !- Minimum Value of y
50.0;                    !- Maximum Value of y

Minimum temperature from the chiller outlet should be as low as (-)10 oC, The range of the leaving CW Temp is set 0 to 20. Is it safe to modify the range to meet the low temperature and get valid performance? The Included Chillers.idf have the curves with even narrower temperature range with the minimum around 4 oC.

I am getting some errors and I suspect they might be due to this limitation.

   ** Warning ** CHILLER:ELECTRIC:REFORMULATEDEIR "COOLSYS1 CHILLER 1": The evaporator outlet temperature (-0.51 C) is outside the range of evaporator outlet temperatures (X var) given in Cooling Capacity Function of Temperature biquadratic curve = WC SCREW DEFAULT 90.1-2004 CAP_FT

 **   ~~~   ** The range specified = 0.00 C to 20.00 C. Environment=TAMPA INTERNATIONAL AP ANN CLG .4% CONDNS WB=>MDB HVAC Sizing Pass 1, at Simulation time=08/21 00:30 - 00:40
** Warning ** CHILLER:ELECTRIC:REFORMULATEDEIR "COOLSYS1 CHILLER 1": The condenser outlet temperature (35.01 C) is outside the range of condenser outlet temperatures (X var) given in Electric Input to Cooling Output Ratio Function of Part-load Ratio bicubic curve = REFORMEIRCHILLER CARRIER 19XR 1259KW/6.26COP/VANES EIRFPLR
 **   ~~~   ** The range specified = 14.56 C to 34.97 C. Environment=TAMPA INTERNATIONAL AP ANN CLG .4% CONDNS WB=>MDB HVAC Sizing Pass 1, at Simulation time=08/21 09:50 - 10:00
*************  ** Warning ** CHILLER:ELECTRIC:REFORMULATEDEIR "COOLSYS1 CHILLER 1": The evap outlet temp range in Cooling Capacity Function of Temp curve error continues.
*************  **   ~~~   **   This error occurred 29559 total times;
*************  **   ~~~   **   during Warmup 0 times;
*************  **   ~~~   **   during Sizing 0 times.
*************  **   ~~~   **   Max=20.  Min=-5.5

*************  ** Warning ** CHILLER:ELECTRIC:REFORMULATEDEIR "COOLSYS1 CHILLER 1": The cond outlet temp range in Electric Input to Cooling Output Ratio Function of PLR curve error continues.

 *************  **   ~~~   **   This error occurred 5118 total times;
 *************  **   ~~~   **   during Warmup 0 times;
 *************  **   ~~~   **   during Sizing 0 times.
 *************  **   ~~~   **   Max=36.465642  Min=4.840225