What EnergyPlus report to use for coil sizing selections?

I need to run loads in OpenStudio 1.11 to size equipment for a commercial 5 story office building. Where in the output reports can I find the following information?

system total cooling coil capacity (MBtu/h) system total heating coil capacity (MBtu/h) system design air flow rate (cfm) outside air flow rate (cfm)

The building will run on district chilled water and have several systems with chilled water fan coils, electric heat, and parellel fan powered boxes. There is also a dedicated outside air system that I need to account for that will deliver neutral air to the air handlers. I am running one zone per system. Here is a screen shot of one of my systems. image description

I have looked in the E+ output report under "Equipment Summary" and "HVAC Sizing Summary" but have found the design loads and nominal total capacities give conflicting information. I understand the coils show design loads with fan and electric power, the nominal capacity does not have fans nor electric power, and the zone sensible is sensible without system effects nor ventilation loads. My "Cooling Coil Nominal Sensible Capacities" are almost double my "Sensible User Design Cooling Loads".

What EnergyPlus report to use for coil sizing selections?

I need to run loads in OpenStudio 1.11 to size equipment for a commercial 5 story office building. Where in the output reports can I find the following information?

system total cooling coil capacity (MBtu/h) (MBtu/h);

system total heating coil capacity (MBtu/h) (MBtu/h);

system design air flow rate (cfm) (cfm);

outside air flow rate (cfm)(cfm);

The building will run on district chilled water and have several systems with chilled water fan coils, electric heat, and parellel fan powered boxes. There is also a dedicated outside air system that I need to account for that will deliver neutral air to the air handlers. I am running one zone per system. Here is a screen shot of one of my systems. image description

I have looked in the E+ output report under "Equipment Summary" and "HVAC Sizing Summary" but have found the design loads and nominal total capacities give conflicting information. I understand the coils show design loads with fan and electric power, the nominal capacity does not have fans nor electric power, and the zone sensible is sensible without system effects nor ventilation loads. My "Cooling Coil Nominal Sensible Capacities" are almost double my "Sensible User Design Cooling Loads".

What EnergyPlus report to use for coil sizing selections?

I need to run loads in OpenStudio 1.11 to size equipment for a commercial 5 story office building. Where in the output reports can I find the following information?

system total cooling coil capacity (MBtu/h);

system total heating coil capacity (MBtu/h);

system design air flow rate (cfm);

outside air flow rate (cfm);

The building will run on district chilled water and have several systems with chilled water fan coils, electric heat, and parellel fan powered boxes. There is also a dedicated outside air system that I need to account for that will deliver neutral air to the air handlers. I am running one zone per system. Here is a screen shot of one of my systems. image description

I have looked in the E+ output report under "Equipment Summary" and "HVAC Sizing Summary" but have found the design loads and nominal total capacities give conflicting information. I understand the coils show design loads with fan and electric power, the nominal capacity does not have fans nor electric power, and the zone sensible is sensible without system effects nor ventilation loads. My "Cooling Coil Nominal Sensible Capacities" are almost double my "Sensible User Design Cooling Loads".