Hi,
Being still a novice in Openstudio I do not know how to properly design HVAC systems. therefore I need help to correctly design one.
For the moment I am using PTAC DX Clg Elec Htg, in reality my AC has no heating. I have hard sized most of the parameters, namely:
OS:ZOneHVAC:PackagedTerminalAirConditioner
- Supply Air Flow Rate During Cooling Operation: 0.431 m^3/s
- Supply Air Flow Rate During Heating Operation: ~ 0 (because no heating)
- Supply Air Flow Rate When No Cooling or heating is Needed: 0 (because in reality the coils are always on when the fan is on, it's in Thailand so it is very hot and humid --> AC is working hard)
- Outdoor Air Flow Rate During Cooling Operation: 0.431 m^3/s
- Outdoor Air Flow Rate During Heating Operation: 0 (because no heating)
- Outdoor Air Flow Rate When No Cooling or heating is Needed: 0 (because in reality the coils are always on when the fan is on, it's in Thailand so it is very hot and humid --> AC is working hard)
OS:Coil:Heating:Electric
- Nominal Capacity: 0 (because no heating)
OS:Fan:ConstantVolume
- Maximum Flow Rate: 0.431 m^3/s (I had to hard size this because every time I ran the simulation it couldn't autosize because there was No "Zone:Sizing" objects even though I had set the Do Zone Sizing Calculation and Do System Sizing Calculation to on in Simulation Control, it works when hard sized)
OS:Coil:Cooling:DX:Single:Speed
- Rated Total Cooling Capacity: 10550 W
- Rated Sensible Heat Ratio: 0.7 (had to hard size, same reason explaine in OS:Fan:ConstantVolume)
- Rated COP 2.8
The rest was left alone.
When I run the simulation with the above parameters it is able to complete, however when I look at HVAC load I have this (0 cooling load).
I've left the Cooling Sizing Parameters and Heating Sizing Parameters to their default values and have not done any design days, I have only used the weather file from the NREL website. I have however made my own Availability Schedule For OS:ZOneHVAC:PackagedTerminalAirConditioner, it is an OnOff Schedule type and looks like this:
However the other Schedules have been left as there default schedule namely:
- Supply Air Fan Operating Mode Schedule for OS:ZOneHVAC:PackagedTerminalAirConditioner: Always On Discrete 17
- Availability Schdule for OS:Coil:Heating:Electric: Always On Discrete 19
- Availability Schdule for OS:Fan:ConstantVolume: Always On Discrete 18
And therefore there isn't any electrical consumption from the PTAC
Any Help Would be greatly appreciated.