DX Single Speed Cooling Coil

Having troubles modelled some basic ACs that are in some of my centre zones. I have the following errors that occur at the beginning of my simulation.

* Warning * CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed="CC AC 6" - Air volume flow rate per watt of rated total cooling capacity is out of range at 1.523E-005 m3/s/W. * ~~~ * Environment=RUN PERIOD 1, at Simulation time=01/01 00:00 - 00:15 * ~~~ * Expected range for VolumeFlowPerRatedTotalCapacity=[2.684E-005--6.713E-005] * ~~~ * Possible causes include inconsistent air flow rates in system components, * ~~~ * or variable air volume [VAV] system using incorrect coil type.

* Warning * CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed "CC AC 6" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -37.38 C. * ~~~ * ...Occurrence info = RUN PERIOD 1, 01/01 00:00 - 00:03 * ~~~ * ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil * ~~~ * 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 16.268 C. * ~~~ * 2) may have a low air flow rate per watt of cooling capacity. Check inputs. * ~~~ * 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.

I have auto sized the ACs and these errors still seem to be occurring. Not sure how to go about fixing them. To create the ACs I used an empty air loop and threw a fan and dx single speed cooling coil on the supply side and the zone with a VAV on the demand side. If there is something wrong with how I modelled this or if anyone has any suggestions that would be greatly appreciated.

Thanks.

DX Single Speed Cooling Coil

Having troubles modelled some basic ACs that are in some of my centre zones. I have the following errors that occur at the beginning of my simulation.

*

   ** Warning * ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed="CC AC 6" - Air volume flow rate per watt of rated total cooling capacity is out of range at 1.523E-005 m3/s/W.
   *   ~~~   * **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=01/01 00:00 - 00:15
   *   ~~~   * **   ~~~   ** Expected range for VolumeFlowPerRatedTotalCapacity=[2.684E-005--6.713E-005]
   *   ~~~   * **   ~~~   ** Possible causes include inconsistent air flow rates in system components,
   *   ~~~   * **   ~~~   ** or variable air volume [VAV] system using incorrect coil type.

* type. ** Warning * ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed "CC AC 6" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -37.38 C. * ~~~ * ** ~~~ ** ...Occurrence info = RUN PERIOD 1, 01/01 00:00 - 00:03 * ~~~ * ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil * ~~~ * ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 16.268 C. * ~~~ * ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. * ~~~ * ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.

inputs.

I have auto sized the ACs and these errors still seem to be occurring. Not sure how to go about fixing them. To create the ACs I used an empty air loop and threw a fan and dx single speed cooling coil on the supply side and the zone with a VAV on the demand side. If there is something wrong with how I modelled this or if anyone has any suggestions that would be greatly appreciated.

Thanks.

DX Single Speed Cooling Coil

Having troubles modelled some basic ACs that are in some of my centre zones. I have the following errors that occur at the beginning of my simulation.

   ** Warning ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed="CC AC 6" - Air volume flow rate per watt of rated total cooling capacity is out of range at 1.523E-005 m3/s/W.
   **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=01/01 00:00 - 00:15
   **   ~~~   ** Expected range for VolumeFlowPerRatedTotalCapacity=[2.684E-005--6.713E-005]
   **   ~~~   ** Possible causes include inconsistent air flow rates in system components,
   **   ~~~   ** or variable air volume [VAV] system using incorrect coil type.

   ** Warning ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed "CC AC 6" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -37.38 C.
   **   ~~~   **  ...Occurrence info = RUN PERIOD 1, 01/01 00:00 - 00:03
   **   ~~~   ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil
   **   ~~~   **    1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 16.268 C.
   **   ~~~   **    2) may have a low air flow rate per watt of cooling capacity. Check inputs.
   **   ~~~   **    3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.

I have auto sized the ACs and these errors still seem to be occurring. Not sure how to go about fixing them. To create the ACs I used an empty air loop and threw a fan and dx single speed cooling coil on the supply side and the zone with a VAV on the demand side. If there is something wrong with how I modelled this or if anyone has any suggestions that would be greatly appreciated.

Thanks.

Edit: Not sure if this will help determine the problem but here is a screenshot of the loop I am using for the ACs.

image description

DX Single Speed Cooling Coil

Having troubles modelled some basic ACs that are in some of my centre zones. I have the following errors that occur at the beginning of my simulation.

   ** Warning ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed="CC AC 6" - Air volume flow rate per watt of rated total cooling capacity is out of range at 1.523E-005 m3/s/W.
   **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=01/01 00:00 - 00:15
   **   ~~~   ** Expected range for VolumeFlowPerRatedTotalCapacity=[2.684E-005--6.713E-005]
   **   ~~~   ** Possible causes include inconsistent air flow rates in system components,
   **   ~~~   ** or variable air volume [VAV] system using incorrect coil type.

   ** Warning ** CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed "CC AC 6" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -37.38 C.
   **   ~~~   **  ...Occurrence info = RUN PERIOD 1, 01/01 00:00 - 00:03
   **   ~~~   ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil
   **   ~~~   **    1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 16.268 C.
   **   ~~~   **    2) may have a low air flow rate per watt of cooling capacity. Check inputs.
   **   ~~~   **    3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.

I have auto sized the ACs and these errors still seem to be occurring. Not sure how to go about fixing them. To create the ACs I used an empty air loop and threw a fan and dx single speed cooling coil on the supply side and the zone with a VAV on the demand side. If there is something wrong with how I modelled this or if anyone has any suggestions that would be greatly appreciated.

Thanks.

Edit: Not sure if this will help determine the problem but here is a screenshot of the loop I am using for the ACs.

image description

I was not sure if I should be adding the outdoor air handler or not.