Fan:VariableVolume Minimum Flow Input

I have taught other EnergyPlus users and observed my own evidence that the Fan:VariableVolume minimum flow inputs, Fan Power Minimum Flow Fraction and Fan Power Minimum Air Flow Rate pertain only to the fan power calculation and do not impact that actual flow during operation. This is consistent with the documentation, but I recently discovered that there seems to be a contradiction when the fan is a return fan located before the outdoor air system.

Here are three idf files. Each has a single VAV air handler with a supply fan and a return fan. This one has no minimum on any fan. This one has a minimum fraction on the supply fan. Finally, this one has a minimum on the return fan, as pictured in the OpenStudio screen shot.

image description

If I graph the supply outlet node mass flow, the simulations with no minimum and a supply minimum stack right on top of each other, however the simulation that has a return fan with a minimum fraction of 0.75 is clearly flow limited. This seems in direct conflict with my expectations and the documentation. Can anyone justify this behavior or confirm that this an EnergyPlus bug?

image description

Fan:VariableVolume Minimum Flow Input

I have taught other EnergyPlus users and observed my own evidence that the Fan:VariableVolume minimum flow inputs, Fan Power Minimum Flow Fraction and Fan Power Minimum Air Flow Rate pertain only to the fan power calculation and do not impact that actual flow during operation. This is consistent with the documentation, but I recently discovered that there seems to be a contradiction when the fan is a return fan located before the outdoor air system.

Here are three idf files. Each has a single VAV air handler with a supply fan and a return fan. This one has no minimum on any fan. This one has a minimum fraction on the supply fan. Finally, this one has a minimum on the return fan, as pictured in the OpenStudio screen shot.

image description

If I graph the supply outlet node mass flow, the simulations with no minimum and a supply minimum stack right on top of each other, however the simulation that has a return fan with a minimum fraction of 0.75 is clearly flow limited. This seems in direct conflict with my expectations and the documentation. Can anyone justify this behavior or confirm that this is an EnergyPlus bug?

image description