Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translate glassdoor to E+.

image description

image description

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translate translates glassdoor to into E+.

image description

image description

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translates glassdoor into E+.

image description

image description

EDIT

Here is the eplus.err

Program Version,EnergyPlus, Version 8.3.0-6d97d074ea, YMD=2015.09.15 16:36,IDD_Version 8.3.0
   ************* IDF Context for following error/warning message:
   ************* Note -- lines truncated at 300 characters, if necessary...
   *************    785 FenestrationSurface:Detailed,
   ************* indicated Name=Sub Surface 1
   ************* Only last 3 lines before error line shown.....
   *************    786   Sub Surface 1,                          !- Name
   *************    787   GLASSDOOR,                              !- Surface Type
   *************    788   ,                                       !- Construction Name
   ** Severe  ** IP: IDF line~788 Error detected in Object=FENESTRATIONSURFACE:DETAILED, name=SUB SURFACE 1
   **   ~~~   ** Field [Construction Name] is required but was blank
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Blank "required" fields found in input
   ** Severe  ** IP: Out of "range" values and/or blank required fields found in input
   **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  0.23sec

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translates glassdoor into E+.

image description

image description

EDIT

Here is the eplus.erreplusout.err

Program Version,EnergyPlus, Version 8.3.0-6d97d074ea, YMD=2015.09.15 16:36,IDD_Version 8.3.0
   ************* IDF Context for following error/warning message:
   ************* Note -- lines truncated at 300 characters, if necessary...
   *************    785 FenestrationSurface:Detailed,
   ************* indicated Name=Sub Surface 1
   ************* Only last 3 lines before error line shown.....
   *************    786   Sub Surface 1,                          !- Name
   *************    787   GLASSDOOR,                              !- Surface Type
   *************    788   ,                                       !- Construction Name
   ** Severe  ** IP: IDF line~788 Error detected in Object=FENESTRATIONSURFACE:DETAILED, name=SUB SURFACE 1
   **   ~~~   ** Field [Construction Name] is required but was blank
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Blank "required" fields found in input
   ** Severe  ** IP: Out of "range" values and/or blank required fields found in input
   **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  0.23sec

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translates glassdoor into E+.

image description

image description

EDIT

Here is the eplusout.err

Program Version,EnergyPlus, Version 8.3.0-6d97d074ea, YMD=2015.09.15 16:36,IDD_Version 8.3.0
   ************* IDF Context for following error/warning message:
   ************* Note -- lines truncated at 300 characters, if necessary...
   *************    785 FenestrationSurface:Detailed,
   ************* indicated Name=Sub Surface 1
   ************* Only last 3 lines before error line shown.....
   *************    786   Sub Surface 1,                          !- Name
   *************    787   GLASSDOOR,                              !- Surface Type
   *************    788   ,                                       !- Construction Name
   ** Severe  ** IP: IDF line~788 Error detected in Object=FENESTRATIONSURFACE:DETAILED, name=SUB SURFACE 1
   **   ~~~   ** Field [Construction Name] is required but was blank
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Blank "required" fields found in input
   ** Severe  ** IP: Out of "range" values and/or blank required fields found in input
   **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  0.23sec

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translates glassdoor into E+.

image description

image description

EDIT

Here is the eplusout.err

Program Version,EnergyPlus, Version 8.3.0-6d97d074ea, YMD=2015.09.15 16:36,IDD_Version 8.3.0
   ************* IDF Context for following error/warning message:
   ************* Note -- lines truncated at 300 characters, if necessary...
   *************    785 FenestrationSurface:Detailed,
   ************* indicated Name=Sub Surface 1
   ************* Only last 3 lines before error line shown.....
   *************    786   Sub Surface 1,                          !- Name
   *************    787   GLASSDOOR,                              !- Surface Type
   *************    788   ,                                       !- Construction Name
   ** Severe  ** IP: IDF line~788 Error detected in Object=FENESTRATIONSURFACE:DETAILED, name=SUB SURFACE 1
   **   ~~~   ** Field [Construction Name] is required but was blank
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Blank "required" fields found in input
   ** Severe  ** IP: Out of "range" values and/or blank required fields found in input
   **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  0.23sec

Simulation failed when building has a glassdoor

I have tested OS without using WWR scrip, simple building in image below. By default, from version 1.6 (may be wrong) OS set a rectangle that touch the bottom of each level as glassdoor and then simulation failed. Changing glass door to fix windows can fix this issue, E+ run fine. (I use VRF system in this case. OS 1.8.5) I think there are something wrong when OS translates glassdoor into E+.

image description

image description

EDIT

Here is the eplusout.err

Program Version,EnergyPlus, Version 8.3.0-6d97d074ea, YMD=2015.09.15 16:36,IDD_Version 8.3.0
   ************* IDF Context for following error/warning message:
   ************* Note -- lines truncated at 300 characters, if necessary...
   *************    785 FenestrationSurface:Detailed,
   ************* indicated Name=Sub Surface 1
   ************* Only last 3 lines before error line shown.....
   *************    786   Sub Surface 1,                          !- Name
   *************    787   GLASSDOOR,                              !- Surface Type
   *************    788   ,                                       !- Construction Name
   ** Severe  ** IP: IDF line~788 Error detected in Object=FENESTRATIONSURFACE:DETAILED, name=SUB SURFACE 1
   **   ~~~   ** Field [Construction Name] is required but was blank
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Blank "required" fields found in input
   ** Severe  ** IP: Out of "range" values and/or blank required fields found in input
   **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  0.23sec