Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. I have also provided the code; can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions.

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J 175901.2156 Environment:Site Outdoor Air Drybulb Temperature C 2.7 Environment:Site Outdoor Air Wetbulb Temperature C 1.332824959 EMS:Zn1_Twb C 12.1110695
Max Outdoor Temperature for Defrost [C] 5
Rated heating capacity [W] 14333.9065
Rated COP 3.837798295 Timestep 60 1 min

Eplus Output
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 26964

My Output MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 27195

Here is my code: def TotCapTempModFac(Tdb): """Calculate Total Capacity Temperature Modification Factor using polynomial coefficients.""" a, b, c, d = 0.758746, 0.027626, 0.000148716, 0.0000034992 return a + b * Tdb + c * Tdb * 2 + d * Tdb * 3

def TotCapFlowModFac(FF): """Calculate Total Capacity Flow Modification Factor using polynomial coefficients.""" a, b, c, d = 0.84, 0.16, 0.0, 0.0 return a + b * FF + c * FF * 2 + d * FF * 3

def EERTempModFac(Tdb): """Calculate EER Temperature Modification Factor.""" a, b, c, d = 1.19248, -0.0300438, 0.00103745, -0.000023328 return a + b * Tdb + c * Tdb * 2 + d * Tdb * 3

def EERFlowModFac(FF): """Calculate EER Flow Modification Factor.""" a, b, c, d = 1.3824, -0.4336, 0.0512, 0.0 return a + b * FF + c * FF * 2 + d * FF * 3

def PLF_curve(PLR): """Calculate Part Load Factor.""" return 0.85 + 0.15 * PLR

def DefrostEIRTempModFac(Twbi,Tdb): """Calculate Defrost EIR Temperature Modification Factor.""" a, b, c, d, e, f = 1,0,0,0,0,0 return a + b * Twbi + c * Twbi * 2 + d * Tdb + e * Tdb * 2 + f * Twbi * Tdb

def DefrostCalc(Tdbo, Twbo, DemandDefrost="OnDemand", tfrac_defrost=None): """Calculate Defrost Energy Input Ratio.

Args:
    Tdbo: Outdoor dry bulb temperature
    Twbi: Outdoor wet bulb temperature
    DemandDefrost: Either "OnDemand" or "Timed" (default: "OnDemand")
    tfrac_defrost: Defrost time fraction — REQUIRED only if DemandDefrost="Timed"

Returns:
    Heating_Capacity_Multiplier: Multiplier for heating capacity during defrost
"""

OutdoorCoilT = 0.82 * Tdbo - 8.589
OutdoorPress = 98600  # Standard atmospheric pressure in Pa
OutdoorHumRat = psychrolib.GetHumRatioFromTWetBulb(Tdbo, Twbo, OutdoorPress)
OutdoorCoildw = max(1e-6, OutdoorHumRat - psychrolib.GetSatHumRatio(OutdoorCoilT, OutdoorPress))

if DemandDefrost == "OnDemand":
    tfrac_defrost = 1 / (1 + (0.01446/OutdoorCoildw))
    Heating_Capacity_Multiplier = 0.875 * (1 - tfrac_defrost)
    Input_Power_Multiplier = 0.954 * (1 - tfrac_defrost)
else:  # Timed defrost
    # Use user-provided fraction, or fall back to common default
    if tfrac_defrost is None:
        tfrac_defrost = 0.058333  # Common EnergyPlus default (≈3.5 min defrost per hour)
    # Else use the provided value (e.g., 0.033 as in your original)
    Heating_Capacity_Multiplier = 0.909 - 107.33 * OutdoorCoildw
    Input_Power_Multiplier = 0.9 - 36.45 * OutdoorCoildw

return Heating_Capacity_Multiplier, Input_Power_Multiplier, tfrac_defrost

Changing parameters

OAT = 2.7 # Outdoor Air Temperature in C Outdoor_WBT = 1.332824959 # Outdoor Wet-Bulb Temperature in C Indoor_WBT = 12.1110695 # Indoor Wet-Bulb Temperature in C Delivered_Load = 175901.2156 # in J

Non-changing parameters

OAT_max_defrost = 5 # Maximum Outdoor Air Temperature for Defrost Operation in C Q_total_rated = 14333.9065 # Rated total capacity in J COP_rated = 3.8377982946518

if OAT <= OAT_max_defrost: Input_Power_Multiplier = DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[1] Q_total = Q_total_rated * TotCapTempModFac(OAT) * TotCapFlowModFac(1) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[0] # W Q_defrost = 0.01 * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[2] * (7.222-OAT) * (Q_total_rated/1.01667) # W PLR = Delivered_Load / (Q_total60) # - PLR = min(1.0, PLR + Q_defrost/Q_total) # - PLF = PLF_curve(PLR) # - RTF = min(1, PLR/PLF) # - P_defrost = DefrostEIRTempModFac(Indoor_WBT, OAT) * (Q_total_rated / 1.01667) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[2] * RTF # W P_heating = 1/COP_rated * Q_total * EERTempModFac(OAT) * EERFlowModFac(1) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[1] * RTF # W else: Input_Power_Multiplier = 1 # set to unity for no defrost operation Heating_capacity_multiplier = 1 # set to unity for no defrost operation Q_total = Q_total_rated * TotCapTempModFac(OAT) * TotCapFlowModFac(1) * Heating_capacity_multiplier # W PLR = Delivered_Load / (Q_total60) # - PLF = PLF_curve(PLR) # - RTF = min(1, PLR/PLF) # - P_heating = 1/COP_rated * Q_total * EERTempModFac(OAT) * EERFlowModFac(1) * Input_Power_Multiplier * RTF # W P_defrost = 0 # W

print(f"Total heating power: {P_heating * 60} J") print(f"Defrost power: {P_defrost * 60} J")

Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. I have also provided the code; can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions.conditions. I have the code here- https://github.com/TM-Abir-Ahsan/untitled-folder/blob/004643820e56b6786d6f479f30c9c098de1938b0/DXHeatingCoil.py#L2

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J 175901.2156 Environment:Site Outdoor Air Drybulb Temperature C 2.7 Environment:Site Outdoor Air Wetbulb Temperature C 1.332824959 EMS:Zn1_Twb C 12.1110695
Max Outdoor Temperature for Defrost [C] 5
Rated heating capacity [W] 14333.9065
Rated COP 3.837798295 Timestep 60 1 min

Eplus OutputOutputs
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 26964

My OutputOutputs MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 27195

Here is my code: def TotCapTempModFac(Tdb): """Calculate Total Capacity Temperature Modification Factor using polynomial coefficients.""" a, b, c, d = 0.758746, 0.027626, 0.000148716, 0.0000034992 return a + b * Tdb + c * Tdb * 2 + d * Tdb * 3

def TotCapFlowModFac(FF): """Calculate Total Capacity Flow Modification Factor using polynomial coefficients.""" a, b, c, d = 0.84, 0.16, 0.0, 0.0 return a + b * FF + c * FF * 2 + d * FF * 3

def EERTempModFac(Tdb): """Calculate EER Temperature Modification Factor.""" a, b, c, d = 1.19248, -0.0300438, 0.00103745, -0.000023328 return a + b * Tdb + c * Tdb * 2 + d * Tdb * 3

def EERFlowModFac(FF): """Calculate EER Flow Modification Factor.""" a, b, c, d = 1.3824, -0.4336, 0.0512, 0.0 return a + b * FF + c * FF * 2 + d * FF * 3

def PLF_curve(PLR): """Calculate Part Load Factor.""" return 0.85 + 0.15 * PLR

def DefrostEIRTempModFac(Twbi,Tdb): """Calculate Defrost EIR Temperature Modification Factor.""" a, b, c, d, e, f = 1,0,0,0,0,0 return a + b * Twbi + c * Twbi * 2 + d * Tdb + e * Tdb * 2 + f * Twbi * Tdb

def DefrostCalc(Tdbo, Twbo, DemandDefrost="OnDemand", tfrac_defrost=None): """Calculate Defrost Energy Input Ratio.

Args:
    Tdbo: Outdoor dry bulb temperature
    Twbi: Outdoor wet bulb temperature
    DemandDefrost: Either "OnDemand" or "Timed" (default: "OnDemand")
    tfrac_defrost: Defrost time fraction — REQUIRED only if DemandDefrost="Timed"

Returns:
    Heating_Capacity_Multiplier: Multiplier for heating capacity during defrost
"""

OutdoorCoilT = 0.82 * Tdbo - 8.589
OutdoorPress = 98600  # Standard atmospheric pressure in Pa
OutdoorHumRat = psychrolib.GetHumRatioFromTWetBulb(Tdbo, Twbo, OutdoorPress)
OutdoorCoildw = max(1e-6, OutdoorHumRat - psychrolib.GetSatHumRatio(OutdoorCoilT, OutdoorPress))

if DemandDefrost == "OnDemand":
    tfrac_defrost = 1 / (1 + (0.01446/OutdoorCoildw))
    Heating_Capacity_Multiplier = 0.875 * (1 - tfrac_defrost)
    Input_Power_Multiplier = 0.954 * (1 - tfrac_defrost)
else:  # Timed defrost
    # Use user-provided fraction, or fall back to common default
    if tfrac_defrost is None:
        tfrac_defrost = 0.058333  # Common EnergyPlus default (≈3.5 min defrost per hour)
    # Else use the provided value (e.g., 0.033 as in your original)
    Heating_Capacity_Multiplier = 0.909 - 107.33 * OutdoorCoildw
    Input_Power_Multiplier = 0.9 - 36.45 * OutdoorCoildw

return Heating_Capacity_Multiplier, Input_Power_Multiplier, tfrac_defrost

Changing parameters

OAT = 2.7 # Outdoor Air Temperature in C Outdoor_WBT = 1.332824959 # Outdoor Wet-Bulb Temperature in C Indoor_WBT = 12.1110695 # Indoor Wet-Bulb Temperature in C Delivered_Load = 175901.2156 # in J

Non-changing parameters

OAT_max_defrost = 5 # Maximum Outdoor Air Temperature for Defrost Operation in C Q_total_rated = 14333.9065 # Rated total capacity in J COP_rated = 3.8377982946518

if OAT <= OAT_max_defrost: Input_Power_Multiplier = DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[1] Q_total = Q_total_rated * TotCapTempModFac(OAT) * TotCapFlowModFac(1) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[0] # W Q_defrost = 0.01 * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[2] * (7.222-OAT) * (Q_total_rated/1.01667) # W PLR = Delivered_Load / (Q_total60) # - PLR = min(1.0, PLR + Q_defrost/Q_total) # - PLF = PLF_curve(PLR) # - RTF = min(1, PLR/PLF) # - P_defrost = DefrostEIRTempModFac(Indoor_WBT, OAT) * (Q_total_rated / 1.01667) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[2] * RTF # W P_heating = 1/COP_rated * Q_total * EERTempModFac(OAT) * EERFlowModFac(1) * DefrostCalc(OAT, Outdoor_WBT, DemandDefrost="OnDemand")[1] * RTF # W else: Input_Power_Multiplier = 1 # set to unity for no defrost operation Heating_capacity_multiplier = 1 # set to unity for no defrost operation Q_total = Q_total_rated * TotCapTempModFac(OAT) * TotCapFlowModFac(1) * Heating_capacity_multiplier # W PLR = Delivered_Load / (Q_total60) # - PLF = PLF_curve(PLR) # - RTF = min(1, PLR/PLF) # - P_heating = 1/COP_rated * Q_total * EERTempModFac(OAT) * EERFlowModFac(1) * Input_Power_Multiplier * RTF # W P_defrost = 0 # W

print(f"Total heating power: {P_heating * 60} J") print(f"Defrost power: {P_defrost * 60} J")

Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. I have also provided the code; can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions. I have the code here- https://github.com/TM-Abir-Ahsan/untitled-folder/blob/004643820e56b6786d6f479f30c9c098de1938b0/DXHeatingCoil.py#L2

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J 175901.2156 Environment:Site Outdoor Air Drybulb Temperature C 2.7 Environment:Site Outdoor Air Wetbulb Temperature C 1.332824959 EMS:Zn1_Twb C 12.1110695
Max Outdoor Temperature for Defrost [C] 5
Rated heating capacity [W] 14333.9065
Rated COP 3.837798295 Timestep 60 1 min

Eplus Outputs
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 26964

My Outputs MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J 27195

Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. I have also provided the code; can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions. I have the code here- https://github.com/TM-Abir-Ahsan/untitled-folder/blob/004643820e56b6786d6f479f30c9c098de1938b0/DXHeatingCoil.py#L2

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J = 175901.2156
Environment:Site Outdoor Air Drybulb Temperature C = 2.7
Environment:Site Outdoor Air Wetbulb Temperature C 1.332824959 EMS:Zn1_Twb = 1.33
Indoor Air Wetbulb Temperature
C 12.1110695
[C] = 12.11 Max Outdoor Temperature for Defrost [C] = 5
Rated heating capacity [W] = 14333.9065
Rated COP = 3.837798295 Timestep = 60 1 min (1 min step)

Eplus Outputs
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 26964

My Outputs MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 27195

Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. I have also provided the code; can Can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions. I have the code here- https://github.com/TM-Abir-Ahsan/untitled-folder/blob/004643820e56b6786d6f479f30c9c098de1938b0/DXHeatingCoil.py#L2

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J = 175901.2156
Environment:Site Outdoor Air Drybulb Temperature C = 2.7
Environment:Site Outdoor Air Wetbulb Temperature C = 1.33
Indoor Air Wetbulb Temperature C [C] = 12.11 Max Outdoor Temperature for Defrost [C] = 5 Rated heating capacity [W] = 14333.9065 Rated COP = 3.837798295 Timestep = 60 (1 min step)

Eplus Outputs
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 26964

My Outputs MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 27195

Coil:Heating:DX:SingleSpeed output mismatch query

For writing an EMS code I am trying to calculate the electrical power draw for a DX:heating coil. Based on the equations mentioned in the Engineering reference I wrote a python code to see if the equations result to the energy plus output. Unfortunately, they don't. Here is the snippet of the simulation variables that was used for calculation along with mine and energyplus outputs. Can anybody point out to what am I doing wrong? The output closely matches electrical energy during no-defrost conditions. conditions but is off by quite a big marging when there are defrost periods. I have the code here- https://github.com/TM-Abir-Ahsan/untitled-folder/blob/004643820e56b6786d6f479f30c9c098de1938b0/DXHeatingCoil.py#L2

Output Variable MAIN DX HEATING COIL_UNIT1:Heating Coil Heating Energy J = 175901.2156
Environment:Site Outdoor Air Drybulb Temperature C = 2.7
Environment:Site Outdoor Air Wetbulb Temperature C = 1.33
Indoor Air Wetbulb Temperature C [C] = 12.11 Max Outdoor Temperature for Defrost [C] = 5 Rated heating capacity [W] = 14333.9065 Rated COP = 3.837798295 Timestep = 60 (1 min step)

Eplus Outputs
MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 63176
MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 26964

My Outputs MAIN DX HEATING COIL_UNIT1:Heating Coil Electricity Energy J = 50499 MAIN DX HEATING COIL_UNIT1:Heating Coil Defrost Electricity Energy J = 27195