Central Cooling Design Supply Air Temperature in Sizing:System

Central Cooling Design Supply Air Temperature in Sizing:System is the design supply air temperature for cooling at the supply air fan outlet in degrees Celsius, isn't it?

Input/Output Reference says it should be the temperature of the air exiting the central cooling coil, but I think the description hasn't been updated for a long time. EnergyPlus takes fan heat into account since V9-0-1. The central cooling coil outlet air temperature is autosized slightly lower than Central Cooling Design Supply Air Temperature in consideration of fan heat.

Central Cooling Design Supply Air Temperature in Sizing:System

Central Cooling Design Supply Air Temperature in Sizing:System is the design supply air temperature for cooling at the supply air fan outlet in degrees Celsius, isn't it?

Input/Output Reference says it should be the temperature of the air exiting the central cooling coil, but I think the description hasn't been updated for a long time. EnergyPlus takes fan heat into account since V9-0-1. The central cooling coil outlet air temperature is autosized slightly lower than Central Cooling Design Supply Air Temperature in consideration of fan heat.