EnergyPlus version 25.1
I am attempting to provide heating using an air-source heat pump for outdoor air temperatures down to -10°C. Below this, a boiler will provide heating to my hot water loop. From the error message shown below, it suggests that negative values are not allowable as an upper limit.
from .err:
* Severe * PlantEquipmentOperationSchemes = "HWL OPERATION", found a negative value for an upper limit in PlantEquipmentOperation:OutdoorDryBulb = "HWL OA CTRL".
* Fatal * LoadEquipList/GetEquipmentLists: Failed due to preceding errors.
my .idf:
PlantEquipmentOperation:OutdoorDryBulb,
HWL OA Ctrl, !- Name
-70, !- Dry-Bulb Temperature Range 1 Lower Limit {C}
-10, !- Dry-Bulb Temperature Range 1 Upper Limit {C}
HWL Boiler, !- Range 1 Equipment List Name
-10, !- Dry-Bulb Temperature Range 2 Lower Limit {C}
70, !- Dry-Bulb Temperature Range 2 Upper Limit {C}
HWL All Equipment; !- Range 2 Equipment List Name
Can I not use negative number in my OA ranges in the PlantEquipmentOperation:OutdoorDryBulb element?
Many thanks for suggestions/observations.