This IES article describes unmet hours troubleshooting. For some reason I cannot upload the image here, but it has a diagram in it to explain how a VAV terminal unit with reheat changes its SA temperature and flow based on RA temperature.
Of particular interest in this diagram is the +/- 2 R throttling range around the heating setpoint and the +/- 2 R throttling range around the cooling setpoint. If I am not too mistaken, the diagram suggests that if the heating setpoint where, say, 70 F and the cooling setpoint were, say, 74 F, then there would no longer be a deadband between cooling and heating.
And, what seems to be more, without adjusting the throttling ranges, if the heating setpoint were to increase above 70 F, and/or the cooling setpoint were to decrease below 74 F, then it may no longer be obvious whether to do cooling or heating for a given RA temperature. This brings me to my question on how EnergyPlus/OpenStudio determines the throttling range.
The ANSI/ASHRAE/IES Standard 90.1-2010 Performance Rating Method Reference in Section 3.5.1 appears to equate throttling range with reporting tolerance, presumably referring to OutputControl:ReportingTolerances, but as far as I can tell, these parameters only determine at what temperature deviation hours are counted as unmet hours.
Thus, is there a way to independently set throttling range in EnergyPlus/OpenStudio, and if so, where would I do that? This question arose, because one of my clients insists on a 70 F heating setpoint and a 72 F cooling setpoint, which at this point I cannot be sure won't cause some sort of trouble.