When autosizing the load for cooling tower by E+, the warnings below were raised: * Warning * Error when autosizing the load for cooling tower = SINGLESPEED COOLING TOWER 2. Tower Design Range Temperature is different from the Design Loop Delta Temperature. * ~~~ * Tower Design Range Temperature specified in tower = SINGLESPEED COOLING TOWER 2 * ~~~ * is inconsistent with Design Loop Delta Temperature specified in Sizing:Plant object = CONDENSER LOOP. * ~~~ * ..The Design Range Temperature specified in tower is = 4.00 * ~~~ * ..The Design Loop Delta Temperature specified in plant sizing data is = 5.00 * Warning * Error when autosizing the UA for cooling tower = SINGLESPEED COOLING TOWER 2. Tower Design Approach Temperature is inconsistent with Approach from Plant Sizing Data. * ~~~ * The Design Approach Temperature from inputs specified in Sizing:Plant object = CONDENSER LOOP * ~~~ * is inconsistent with Design Approach Temperature specified in tower = SINGLESPEED COOLING TOWER 2. * ~~~ * ..The Design Approach Temperature from inputs specified is = 2.00 * ~~~ * ..The Design Approach Temperature specified in tower is = 4.00
For the 1st warning, translate error from OpenStudio osm file was suspected as In osm: 4, !- Design Approach Temperature {deltaC} 5, !- Design Range Temperature {deltaC} In idf translated from osm: 4, !- Design Approach Temperature {deltaC} 4, !- Design Range Temperature {deltaC} For such error, I think maybe it should be fixed by OpenStudio.
For the 2nd warning, no clue was found. Have anyone encountered similar warnings? My soft versions: OpenStudio App: 1.7.2 OpenStudio: 3.7.0 EnergyPlus: 23.2