Beware of Optimum Start (CBECC)
This is more of a word of caution than a question, although feel free to share insights if it helps others deal with this interesting aspect of CBECC / EnergyPlus modeling.
I noticed when working on a T24 compliance model using CBECC 2022 that the supply airflow and fan power were peaking at 4am for the Proposed model, and 7am for the Baseline. I decided to untick the "Optimum Start" box for the proposed VAV Reheat AHUs and voila! My compliance margin jumped from -7.3% (failing) to +3.5%.
I reviewed the IDF file and the EnergyPlus Engineering Reference (link) and the AvailabilityManager:OptimumStart
was created and applied similarly in both models, using AdaptiveTemperatureGradient
as the method. Full object descriptor below.
The moral of the story for me is: default to OFF for optimum start in this lovely compliance software. Also, never trust "optimum" or a checkbox that represents a complex sequence of operations.
AvailabilityManager:OptimumStart,
Availability Manager Optimum Start 1, !- Name
Always On Discrete, !- Applicability Schedule Name
AssemblyHVACAvail, !- Fan Schedule Name
MaximumofZoneList, !- Control Type
, !- Control Zone Name
Availability Manager Optimum Start 1 Control Zones List, !- Zone List Name
3, !- Maximum Value for Optimum Start Time {hr}
AdaptiveTemperatureGradient, !- Control Algorithm
3, !- Constant Temperature Gradient during Cooling {deltaC/hr}
3, !- Constant Temperature Gradient during Heating {deltaC/hr}
1.66666666666667, !- Initial Temperature Gradient during Cooling {deltaC/hr}
1.66666666666667, !- Initial Temperature Gradient during Heating {deltaC/hr}
2, !- Constant Start Time {hr}
2; !- Number of Previous Days {days}