Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Zone sensible and latend load

asked 2024-06-17 11:40:41 -0500

updated 2024-06-18 10:32:28 -0500

How can I view the sensible and latent load of each thermal zone in OpenStudio?

I am still looking for a report similar to system check sums in Trace700 but I can not find it in Openstudio.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2024-07-26 06:36:50 -0500

If for instance you're after internal "latent loads" (see here), you can request an annual tally :

image description

... and look up the results (in J) in the ESO file. You can do the same for infiltration latent loads, as well as sensible (and/or total) loads, and so on.

I think generating a concise table (in OpenStudio) from selected latent + sensible load components would require an EnergyPlus measure or customizing the OpenStudio Results Measure.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2024-06-17 11:40:41 -0500

Seen: 155 times

Last updated: Jul 26