Why can't I heat and cool at the same time in Transys

asked 2024-05-26 07:36:40 -0600

chloe's avatar

updated 2024-05-28 10:55:19 -0600

Why can't I heat and cool at the same time in Transys?? Is it possible?

edit retag flag offensive close merge delete

Comments

@chloe can you provide a bit more detail? What kind of heating cooling system(s) are you modeling? Do you want heating in some zones and cooling in other zones at the same time?

Also, can you upload your model to Google Drive, Dropbox, etc. and then share a URL for others to download? That would help others provide better solutions.

Aaron Boranian's avatar Aaron Boranian  ( 2024-05-27 12:02:21 -0600 )edit

Do you want heating in some zones and cooling in other zones at the same time? -> Yeees!! . I have to make vrf system. So I need the answer of my question. let me know about that.

chloe's avatar chloe  ( 2024-05-28 07:27:25 -0600 )edit

@chloe I'm not a TRNSYS user, but usually the VRF condenser (aka outdoor unit) has a heat recovery option. If this heat recovery is off, then all zones with VRF terminals (aka indoor units) connected to the same VRF condenser will either receive heating or cooling -- the only way to enable a mix of heating and cooling across these zones is to turn on heat recovery.

Aaron Boranian's avatar Aaron Boranian  ( 2024-05-28 10:57:06 -0600 )edit