Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Why is my During Heating unmet hours measurement much higher than my During Occupied Heating unmet measurement?

asked 2024-05-03 19:18:37 -0600

Mike117's avatar

updated 2024-05-04 09:27:50 -0600

I have tried changing the following parameters:

  • Lighting schedule
  • Clothing schedule
  • Occupancy schedule
  • thermal zone design supply air temperature (increase heat)
  • Temperature setpoint

The During Heating measurement has remained the same throughout every change. Table below:

image description The Simple ASHRAE 55-2004 HAS +7000 UNMET hours mostly because of clothing schedules which I will change.

Is there any information that maybe necessary to help diagnose the issue? I checked the sizing parameters and they all seem to fine to me.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2024-05-06 15:23:52 -0600

Craig Simmons's avatar

Probably has to do with the nighttime operational control of the HVAC system. Generally "Occupied" are the more important ones (for ASHRAE compliance, etc.) but it is good to be sure your unoccupied HVAC control is correct. Where you review/input that control depends on the type of HVAC system you are modeling.

Clothing schedules will not impact these unmet hours, these are purely related to dry-bulb temperature of the zone compared to the thermostat setpoint. There's a separate table for comfort metrics.

edit flag offensive delete link more

Comments

Where can I find the table for comfort metrics?

That makes way more sense. I do not have the simulation running during the night, At night, the HVAC system is meant to turn on every 2 hours depending on zone temperatures, I care for worst case energy demand.

Mike117's avatar Mike117  ( 2024-05-06 17:29:20 -0600 )edit

It's in the eplusout.html report, called "Comfort and Setpoint Not Met Summary". However it just gives one number for time not comfortable based on "Simple ASHRAE 55-2004", probably inadequate if you're doing anything more than the most basic analysis.

There may be others in this forum that can give more specific advice. I would recommend reading the EnergyPlus "Input Output Reference". You may also find you need to move into measure writing to do something comprehensive

Craig Simmons's avatar Craig Simmons  ( 2024-05-07 08:02:22 -0600 )edit

There is this measure in the common-measures-gem (found on the BCL) https://bcl.nrel.gov/content/5ae7b6b3...

Also you'll want to figure out which reports to add for analysis and trouble-shooting. Also found in the Input Output Reference.

Craig Simmons's avatar Craig Simmons  ( 2024-05-07 08:18:26 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2024-05-03 19:18:37 -0600

Seen: 359 times

Last updated: May 06