Zone Air Chiller Total Cooling Rate vs Zone Air Chiller Zone Total Cooling Rate

asked 2024-04-18 09:53:16 -0600

Zakaria's avatar

Hello everyone,

I was looking at Output parameters, specifically the cooling rate of air-chiller - called Loading Zone AirChiller - used in a zone - called Loading Zone - and I found 3 values, two of which are equal and the third one is greater.

Can anyone explain the difference between these output variables?

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-04-20 22:31:19 -0600

One is for the system (most likely the highest number since it has additional defrost losses to make up), another is for the total of the zone loads, and a third is for each zone (it appears you only have one zone?). If you had several zones attached to this one system, it would report the load for each one. The outputs for this object can be found here: https://bigladdersoftware.com/epx/doc...