Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Modeling an inverter based AC as a VRF

asked 2024-03-20 02:37:29 -0600

hk65's avatar

updated 2024-03-20 15:26:45 -0600

I modeled the inverter based AC as a VRF, but the simulated VRF energy consumption values are much higher than measured values of the inverter based AC. I tried changing the partload ratio curve coefficients because the load in the room is very small. It did not work. any suggestions?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2024-03-20 15:34:34 -0600

Probably should be using cycling fan mode and also check the cooling EIRfPLR curve to make sure it represents the VS compressor energy. VRF will use a different curve. See figure 10 in https://www.fsec.ucf.edu/en/publicati.... The VS AC EIRfPLR curve will go lower than the one shown in the figure (blue line) and cross at 0,0.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2024-03-20 02:37:29 -0600

Seen: 90 times

Last updated: Mar 20