Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Thermal zone's annual heating and cooling load

asked 2024-03-13 03:10:00 -0600

updated 2024-03-13 09:30:12 -0600

Hello, I was wondering if anyone could assist me in obtaining the annual thermal zone contributions to the total HVAC load from the OpenStudio Results. The heating and cooling load of each thermal zone for the entire year is what I am looking for, instead of the monthly heating and cooling loads displayed in the OpenStudio Result. Any guidance would be greatly appreciated. Thank you in advance. I am using OpenStudio.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-03-15 06:50:06 -0600

Erfi's avatar

To calculate for a specific zone rather than the entire building, you can condition just the targeted area while leaving the other zones unconditioned.

edit flag offensive delete link more

Comments

Thank you very much. I have tried the suggested method, but it did not give me the required values. For example, when I added up the heating load of all the thermal zones when each one was conditioned individually, it did not match the total heating load of the entire building when all the thermal zones were conditioned together. Additionally, I noticed that when only one thermal zone (thermal zone 1) was conditioned while the others were not, the air temperature of an unconditioned thermal zone (thermal zone 2) was not the same as when the entire building was unconditioned.

ngwu.chris.2@gmail.com's avatar ngwu.chris.2@gmail.com  ( 2024-03-17 23:27:00 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2024-03-13 03:10:00 -0600

Seen: 104 times

Last updated: Mar 13