Seasonal thermostat setpoints / EnergyPlus

asked 2023-12-24 18:28:56 -0600

Uthman's avatar

updated 2023-12-26 08:17:17 -0600

Hello,

I am trying to put some setup for the HVAC system:

  1. I want the cooling mode to be running from May 1st until Oct 1st the setpoint should be 25C° the Heating would be on if the temp goes below 16C°.
  2. The heating mode should be on from Oct 1st Until May 1st the setpoint should be 22C°and the cooling would be on if the temp went above 30C.

How can I do that ?? I am learning but this thing was difficult.

edit retag flag offensive close merge delete

Comments

For which application?

Denis Bourgeois's avatar Denis Bourgeois  ( 2023-12-25 07:10:20 -0600 )edit

Hello, EnergyPlus

Uthman's avatar Uthman  ( 2023-12-25 08:08:35 -0600 )edit

1 Answer

Sort by » oldest newest most voted
4

answered 2023-12-26 08:21:22 -0600

updated 2023-12-27 08:47:59 -0600

@Uthman, try the following (here, for a zone named "Office"):

ScheduleTypeLimits,  Temperature, -60, 200, CONTINUOUS;
ScheduleTypeLimits, Control Type,   0,   4, DISCRETE;

Schedule:Constant,
  Office Control Type Schedule,
  Control Type,                    !- Schedule Type Limits
  4;                               !- Dual Setpoint

ZoneControl:Thermostat,
  Office Thermostat Control,
  Office,                          !- Zone
  Office Control Type Schedule,    !- Control Type Schedule
  ThermostatSetpoint:DualSetpoint, !- Control Object Type
  Tstat;                           !- Control Object

ThermostatSetpoint:DualSetpoint,
  Tstat,
  Office Heating Setpoints,        !- Heating Setpoint Schedule
  Office Cooling Setpoints;        !- Cooling Setpoint Schedule

Schedule:Compact,
  Office Heating Setpoints,        !- Heating Setpoint Schedule
  Temperature,                     !- Schedule Type Limits
  Through: 4/30,
    For: AllDays,
    Until: 24:00, 22.0,
  Through: 9/30,
    For: AllDays,
    Until: 24:00, 16.0,
  Through: 12/31,
    For: AllDays,
    Until: 24:00, 22.0;

Schedule:Compact,
  Office Cooling Setpoints,        !- Cooling Setpoint Schedule
  Temperature,                     !- Schedule Type Limits
  Through: 4/30,
    For: AllDays,
    Until: 24:00, 30.0,
  Through: 9/30,
    For: AllDays,
    Until: 24:00, 25.0,
  Through: 12/31,
    For: AllDays,
    Until: 24:00, 30.0;

It's pretty basic (e.g. no daily setbacks, no difference between weekdays vs weekends). Adapted from the example provided here (just before "Output"). Hope this is close to what you're after.