Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Error with consumptions and outside temperature

asked 2023-11-25 15:55:54 -0500

Pablocm's avatar

updated 2023-11-27 09:33:25 -0500

Hello, I have the following error in open studio.

As attached in the image in february the temperature is lower than in december, but the heating consumption is higher in december. This does not make sense.

Does anyone know why?

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2023-11-26 06:11:55 -0500

For non-leap years, February has 3 less days than December. Based on your results, the average daily heating load in February (28 days) is 11.42 kWh/day, while the average in December (31 days) is 11.47 kWh/day (at 20 cents/kWh, that's roughly 1 cent/day).

In addition, February typically has more sunlight than in December (Northern Hemisphere):

image description

This would be enough to tilt the balance towards less heating in February than in December in many locations and for many building types. This would not be the case everywhere; in my (much colder) neck of the woods, it is on average ~5K colder in February than in December; despite being sunnier, it is not unusual to heat more in February (than in December). This is just scratching the surface ...

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-11-25 15:55:54 -0500

Seen: 54 times

Last updated: Nov 26 '23