Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Different results in Ideal Loads if I calculate the ventilation + infiltration load all together at the zone level than if I calculate the infiltration at the zone level and the ventilation at the system level.

asked 1 year ago

jrgros's avatar

updated 1 year ago

Different results in Ideal Loads if I calculate the ventilation + infiltration load all together at the zone level than if I calculate the infiltration at the zone level and the ventilation at the system level. What is this about? Makes sense?

Ventilation + infiltration load all together. End Use Consumption (kWh) Heating 2,139 Cooling 306

Infiltration at the zone level and the ventilation at the system level. End Use Consumption (kWh) Heating 1,739 Cooling 319

If you want, I can send you the two OSM files so you can check it yourself. We are talking about 23% more energy simply by introducing all the outside air as infiltrations. Such a difference seems strange to me.

CASE 1 SpaceInfiltrationdesignflowrate 1.26 ACH CASE 2 SpaceInfiltrationdesignflowrate 0.26 ACH DesignSpecificationOutdoorAir 1.00 ACH

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
0

answered 1 year ago

gianfra's avatar

What are the reporting outputs?

Preview: (hide)
link

Comments

With the same building I have simulated the building by placing all the outside air in SpaceInfiltrationdesignflowrate and with openstudio it gives me this results in End Use Use Consumption (kWh) Heating 2,186 Cooling 319.

Then with the same building I have simulated the building separating the outside air in SpaceInfiltrationdesignflowrate and DesignSpecificationOutdoorAir and with openstudio it gives me this results in End Use Use Consumption (kWh) Heating 1,789 Cooling 333.

I have used OpenStudio together with the Ideal Air Loads HVAC measure.

jrgros's avatar jrgros  ( 1 year ago )

Make sure you defined the DesignSpecification:OutdoorAir object into the Ideal Air Loads object. Check the idf file.

gianfra's avatar gianfra  ( 1 year ago )

It is defined in the idf file. Energyplus must calculate differently when the air enters the thermal zone through infiltration than when the air enters through mechanical ventilation. The strange thing is that there is such a difference.

jrgros's avatar jrgros  ( 1 year ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 1 year ago

Seen: 587 times

Last updated: Oct 11 '23