… 90.1 2022 requirements for linear thermal bridges

asked 2023-10-03 12:38:27 -0500

updated 2023-10-04 10:14:16 -0500

Hi everyone. We'll soon release v3.3.0 of the OpenStudio Measure TBD. Code changes include support for ASHRAE 90.1 2022, such as differentiating:

  • intermediate floor-to-wall intersections
  • attached balcony (often cantilevered) edges
  • balcony-to-vertical-fenestration edges (e.g. full height glazing, sliding doors)

Changes made, tests are green. However, we do have interpretation questions concerning 90.1 2022. Feedback/answers to any of these questions are quite welcome, and may drive final adjustments before release. Questions pertain to more than one compliance path, e.g. Energy Cost Budget Method (ECB, Section 12), Performance Rating Method (PRM, Appendix G). To keep things simple, we focus here on linear thermal bridging requirements for ECB (PSI-factors). First, an excerpt of 90.1 2022 (Table A10.1, in SI units):

90.1 2022 Table A10.1

PSI-factor thresholds differ based on above-grade wall construction (e.g. steel-framed, vs mass, vs wood-framed). Values are provided for both mitigated (default) and unmitigated intersections (or edges), with mitigated values reflecting Section 5 prescriptive requirements (largely descriptive in nature). In a nutshell, ECB requires that listed edges in Table A10.1 be modelled in the Budget Building Design (BBD), if included in the Proposed Design (PD). The BBD shall retain the mitigated PSI-factors in Table A10.1, and have clear-field U-factor adjustments (or be "derated"), as per Section A10.2. Modellers may opt to apply Table A10.1 mitigated or unmitigated PSI-factors for the PD (depending on project details) or instead rely on other sources (such as the BETBG, ISO 14683, test lab results). Development branch v278 (to be released as TBD v3.3.0 once merged):

  • includes Table A10.1 PSI-factors and CHI-factors
  • identifies/tracks A10.1 listed (and unlisted) edges from OpenStudio model geometry
  • automatically derates OpenStudio surface construction clear-field U-factors (per A10.2)

Q1 : TBD identifies/tracks a wider range of linear thermal bridge types than those listed in A10.1. We're unsure if the intention with 90.1 is to exclude these unlisted edges (e.g. corners) altogether, or to process them separately (see Q5 on requirement 5.5.5.5). For the moment, when selecting 90.1 2022 PSI-factor sets, TBD tracks omitted edges (like corners), yet by default applies a PSI-factor of 0 W/K per linear meter. This basically cancels the derating (or bridging) effect of excluded edges, in principle for both BBD and PD models. Are we correct in our interpretation: that 90.1 sets aside such edges? Should we consider unlisted edges as unregulated when applying 90.1, similar to process loads? Answers to Q5 may lead us to a completely different interpretation/solution. Note that with large/simple big box retail or warehouse models, we may encounter half a dozen corner edges (where their combined effect may be quite modest). Yet the impact of corner edges may become significant (!) with highly articulated façade designs (e.g. MURBs with bay windows, niches).


Q2 : In relation to Q1, why such exclusions? Users often need guidance, and knowing why helps. The list of omitted edge ... (more)

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2025-05-05 07:55:33 -0500

From the above questions, and relying on advice from experienced modellers (for which I’m very grateful), I ended up sending 4 related interpretations/questions to ASHRAE back in 2024. Questions were reformulated so each answer could be a simple "YES" or "NO". The entire process, including meetings and email threads, took 12 months. ASHRAE published Interpretation IC 90.1-2022-6 OF in April 2025, see here. I’m very grateful to ASHRAE and active committee members for their time, effort and patience. Good news is that there is some much needed clarity for energy modellers. Bad news is that there is still a fair amount of uncertainty for modellers regarding requirement 5.5.5.5. Here’s my overview - hope this helps.


The initial Q1, Q2 & Q3 above were attempts to better circumscribe the scope of 5.5.5.5. In a nutshell, do linear thermal bridges NOT listed under 5.5.5.1 through 5.5.5.4 systematically fall under the scope of 5.5.5.5.? ASHRAE’s answer to Interpretation #1 is "YES" - all other linear thermal bridging fall under 5.5.5.5.’s umbrella. This includes corners, perimeters around unfenestrated doors, demising wall edges, etc. These are lumped in with point conductances like columns, anchors for signage or fixed shading, etc. There are exceptions, such as individual thermal bridges having material thermal conductivities less than 0.433 W/m·K (e.g. wood, acrylic, fibreglass, rubber). Let's call this exemption A. For non-exempted (conductive) materials like concrete, steel or aluminium, individual point thermal bridges (e.g. columns, anchors) may still be exempted if their cross-sectional area is under the following thresholds:

image description

Let's call this exemption B. If exempted (via A or B), modellers need not consider such benign thermal bridges in their models. To be exempted, e.g.:

  • cylindrical concrete columns would have to be no more than 150mm (6in) in diameter
  • cylindrical steel tubes (9mm thickness) could be no more than 200mm (8in) in diameter

Such diameters would not be enough for most structural applications, e.g. ground-floor colonnade, like the Seagram Building on NY’s Park Avenue (left), the N2 building in London (bottom-right) or the Palazzo Ducale (top-right) - fairly common archetype.

image description

Stronger (non-exempted) columns would therefore need to be accounted for using Equation 5.5.5.5 (see above Q5), as confirmed by ASHRAE’s answer to Interpretation #2. Consider the following (compliant) hypothetical building, as an Equation 5.5.5.5 case study:

  • new, fully heated/cooled building
  • 3 above-grade storeys, 50m x 100m in floor area, 5m floor-to-floor height
  • climate zone 4 (or colder)
  • conventional commercial roofing, e.g. semi/rigid insulation over decking

The above-grade area of the building envelope in Equation 5.5.5.5 would be 9,500 m2, giving a whole-building threshold of 14.3 (i.e. left-side of Equation 5.5.5.5). I consider either side of Equation 5.5.5.5 as indices (no units).

Switching over to the ... (more)