Questions related to the cooling load calculations and selecting the right equipment size.

asked 1 year ago

awadhi's avatar

updated 1 year ago

1- How does the BEopt determine the AC tonnage size ? Does it follow manual J and select the 99% design load? If so, what about the solar heat gain. Does it use the highest solar heat gain day throughout the year or it uses the solar heat gain at the 99% design day ?

2- In case it uses the 99% design load, let's say for example it is 4 ton. Is the 4 ton capacity rated at outdoor temperature 95F ? Meaning that at higher ambient temperatures the unit will deliver less cooling capacity ?

3- What curve is being used in BEopt to account for the unit performance degradation? Is it similar to the NREL curve published in 2013 "Improved Modeling of Residential Air Conditioners and Heat Pumps for Energy Calculations".

4- Can I track the unit cooling capacity every hour ?

5- What is the indoor wet-bulb temperature when we change the indoor setpoint (e.g., 70F, 71F, ...). And if it is changing, are we able to monitor the indoor wet-bulb temperature ?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 1 year ago

  1. Yes, it follows ACCA Manual J/S using the 1%/99% design temperatures. Corresponding design loads, broken out by component (windows, walls, ducts) can be viewed in the End Use graph. I'm not sure I understand your question about solar heat gain, it follows the ACCA methodology (which is not using the highest solar of the year nor the value from a specific design day).

  2. Correct. The reported capacity is the nominal/rated capacity and the AC will have reduced output capacity at higher temperatures.

  3. Yes, it uses those curves for 1-speed and 2-speed systems.

  4. If you request timeseries output, you can see the cooling energy delivered for every timestep.

  5. BEopt v3 does not report the indoor wetbulb temperature. You'll have to take the EnergyPlus input file, add a request for that output variable, and re-run it directly in EnergyPlus.