Openstudio standards - Whole Buildings

asked 2023-09-12 03:14:26 -0600

updated 2023-09-14 09:37:28 -0600

Looking for advice on how to use openstudio-standards for space types that do not have the Whole building option.

Some building types (Office for example) have an option for whole building when determining the space_type_ratios from the building_type. However, most do not have it.

I am coding a very simplifided model for a hospital and this is one of the buildling types that do have the whole building type unfortunately. I can understand why of course. Hospitals are complicated.

I am considering two potential approaches:

  1. Use a different standard like NECB (I am using ASHRAE 2013 at the moment) as these seems to have the whole building option for hospital.
  2. Use blend_space_types_from_floor_area_ratio and blend_internal_loads from OsLib_ModelSimplification

The latter seems to be the approach in some of the measures

Any recommendation?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2023-11-06 16:25:30 -0600

If you blend loads in a hospital, you are going to get high internal loads from MRI rooms getting exhausted with the high ventilation rates coming from the operating rooms. I think you are better off assuming space type ratios for the different kinds of space types and not trying to blend them together.

edit flag offensive delete link more

Comments

Good point. Thanks

MapMortar's avatar MapMortar  ( 2023-11-07 09:46:22 -0600 )edit