E+ get HVAC Electricity Consumption per Zone?

asked 2023-09-01 11:51:27 -0600

LeSUTHU's avatar

updated 2023-09-03 09:57:53 -0600

Hello,

I am using pyenergyplus api, and was wondering how can I get the HVAC electricity consumption per zone? More specifically, I wish to get the cooling load spent per zone for each timestep.

Thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2023-09-05 09:21:46 -0600

If you specifically want cooling load per thermal zone, you can add a ZoneHVAC:IdealAirSystem to each thermal zone. When using it, you may want to disable outdoor air, dehumidification, and humidification. Then look at the Zone Air System Sensible Cooling Energy for timestep output.

edit flag offensive delete link more

Comments

See https://unmethours.com/question/41799... for some prior discussion

shorowit's avatar shorowit  ( 2023-09-05 13:35:49 -0600 )edit