Generating chillers performance curves with manufacturer data

asked 2023-08-23 20:34:00 -0600

larry liong's avatar

updated 2023-08-25 15:33:53 -0600

I am trying to generate the Energyplus chiller performance curves CoolCapfT, CFIRfT, and CFIRfPLR using the data provided by the manufacturer. But I am not quite sure if the columns are enough, can anyone guide me on the process?

Chiller Performance Data:

pct load: 100, cap(TR): 455, pct power: 100, input power (kW): 172, EEFT (°F): 68, CEFT: 85.10, CLFT (°F): 93.90, sys perf (kW/TR): 0.378

pct load: 66, cap(TR): 300.3, pct power: 62.8, input power (kW): 108, EEFT (°F): 64.33, CEFT: 85.10, CLFT (°F): 90.88, sys perf (kW/TR): 0.360

pct load: 33, cap(TR): 150.2, pct power: 36.6, input power (kW): 63, EEFT (°F): 60.76, CEFT: 85.10, CLFT (°F): 88.02, sys perf (kW/TR): 0.419

pct load: 16.8, cap(TR): 76.3, pct power: 24.4, input power (kW): 42, EEFT (°F): 59.01, CEFT: 85.10, CLFT (°F): 86.62, sys perf (kW/TR): 0.550

edit retag flag offensive close merge delete