Can i draw different ceiling height in the same floor on openstudio application?

asked 2023-08-10 14:50:20 -0600

payam's avatar

updated 2024-10-18 11:51:50 -0600

I want to model a building which has open spaces in some areas. i.e. in some areas in floor one, the ceiling height is different from others. is there a way to draw it inside of openstudio without using the sketchup ?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
3

answered 2023-08-11 10:45:43 -0600

Yes, you can do this directly in the OpenStudio App:

1) Click on the >> button to allow space-specific properties.

image description

2) Type in different values for e.g. Floor to Ceiling Height.

image description

3) When you go to the 3D geometry rendering, it should reflect the height difference.

image description

edit flag offensive delete link more

Comments

Thank You, I really appreciate it !

payam's avatar payam  ( 2023-08-11 15:33:03 -0600 )edit
1

answered 2023-08-11 07:03:08 -0600

I'm assuming that "to draw it inside of OpenStudio" (not SketchUp) means the FloorspaceJS editor. I'm only somewhat familiar with the editor - hopefully experienced users will correct me with editor subtleties that may simplify the following steps.


This is how I would approach a 2-storey lobby using the editor. The editor-generated lobby below is made up of 2x superimposed spaces ("Space 1-2" & "Space 2-2"), each with their own unique thermal zone. The selected interzone Floor, "Face 18" (of "Space 2-2"), is matched with an interzone RoofCeiling, "Face 7" (in "Space 1-2" below).

Lobby intermediate Floor/RoofCeiling

Adding a new AirBoundary Construction.

AirBoundary

Assigning the new AirBoundary Construction to "Face 18" and "Face 7".

AirBoundary assignment

Making sure "Space 2-2" is not part of the total floor area.

image description

I'd then start going over inter alia:

  • the split in lobby lighting (between "Space 1-2" vs "Space 2-2")
  • the Air Boundary Construction air exchange (between "Space 1-2" & "Space 2-2")
  • whether the upper part of the lobby ("Space 2-2") is (directly) mechanically ventilated/exhausted
  • whether the upper part of the lobby ("Space 2-2") holds heating equipment
  • and so on ...

That's a simple case. Depending on the configuration and E+ version, you may trip over a few hurdles (e.g. this fix a year ago). I'd suggest incremental experimentation.

edit flag offensive delete link more

Comments

Thank you Denis!

payam's avatar payam  ( 2023-08-11 15:31:59 -0600 )edit