@kbk78,
So, I did some digging today with your example file. Unfortunately it has revealed some issues with that operation scheme that are going to require a workaround if you need to use this before the next release of E+.
I have opened an issue on our GitHub site here that details what I have seen so far today. If you have a GitHub account, please feel free to engage in the conversation on that issue. This is a high priority to me, so I anticipate having the issues fixed up soon, but the fix won't be available in a major release until our September 30 release.
In the meantime, if you need an immediate workaround, you could simply pull the outdoor dry bulb from the weather file for every hour, and then create an hourly 0/1 schedule for when the temperature is above or equal to the switch temperature, then one for when it is below. These schedules could be used in the CondenserEquipmentOperationSchemes object to schedule two separate PlantEquipmentOperation: instances. Of which neither should be the OutdoorDryBulb. I would imagine something like:
CondenserEquipmentOperationSchemes,
Condenser_Loop Operation, !- Name
PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
AboveScheme, !- Control Scheme 1 Name
AboveSchedule, !- Control Scheme 1 Schedule Name
PlantEquipmentOperation:CoolingLoad, !- Control Scheme 2 Object Type
BelowScheme, !- Control Scheme 2 Name
BelowSchedule; !- Control Scheme 2 Schedule Name
where the AboveSchedule/BelowSchedule are the values you created above outside of E+. (You could use Schedule:File for convenience there). Then the operation schemes would look like:
PlantEquipmentOperation:CoolingLoad,
AboveScheme, !- Name
0, !- Load Range 1 Lower Limit {W}
100000000, !- Load Range 1 Upper Limit {W}
CoolingTower Equipment List; !- Range 1 Equipment List Name
PlantEquipmentOperation:CoolingLoad,
BelowScheme, !- Name
0, !- Load Range 1 Lower Limit {W}
100000000, !- Load Range 1 Upper Limit {W}
FluidCooler Equipment List; !- Range 1 Equipment List Name
Thanks for helping identifying this.
So, after the comment by @kbk78, it is clear that there is a set of issues that need to be addressed, and this isn't the location for the conversation to figure it all out (and it will be a lengthy process to work through them all). I would recommend that we close this conversation and continue to work out all the issues together on the GitHub issue page if you already have or are willing to register on GitHub. If you are satisfied with that, please take this as the final answer for the UnmetHours conversation, and we'll work to address this over on the other side.
Should be sufficient, some additional info could help resolve the problem.
What's your pumping scheme? What is the pump size compared to the design flows of the two units? Do you have a supply side bypass on the condenser loop?
Thanks for your Response, There is a variable speed Pump on the Supply Side That is autosized. Also there is a Bypass on the supply side. What is Even more surprising is that I set the CondenserEquipmentOperationScheme Schedule to Off and the Condenser equipment still runs. These controls seem to have no impact on the condenser Loop operation.
Which version of E+ are you using?
Was using 8.1. Just updated this to version 8.3 and having the same problems. I have attached the file above if you could look at it (Rename .gif to .idf) . It uses LoadProfile to simulate the plant load.