Trouble with the HVAC setting

asked 2015-07-22 05:08:44 -0600

Elena Guidolin's avatar

updated 2020-06-16 14:04:48 -0600

Dear all,

I am simulation a building using Openstudio and E+. The HVAC system is composted by a multifunctional heat pump (it makes simultaneously heating and cooling), a ground water condenser and cooled beams as air terminals that provided both the cooling and the heating in the zones. I have used the CentralHeatPumpSystem to simulate the multifunctional heat pump. I have used the PlantComponent:TemperatureSource to simulate the ground water used as condenser I have used the FourPipeInduction Air terminals to simulate the cooled beams. I can't understand why the simulation doesn't work properly and I have problems with the sizing of the objects and the convergence of the temperature.

Has someone of you any idea how should I do to solve this issue? I attach the idf below.

Thank you very much

Have a nice day

Elena

part of the error message:

************* Beginning System Sizing Calculations
************* Beginning Plant Sizing Calculations
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 2
**   ~~~   ** the apparatus dew-point is below the coil design inlet water temperature;
**   ~~~   ** the coil outlet design conditions will be changed to correct the problem.
**   ~~~   ** The initial design conditions are: Tair,in = 25.9833
**   ~~~   **                                    Wair,in = 9.554298E-003
**   ~~~   **                                    Twater,in = 7.2200
**   ~~~   **                                    Tair,out = 9.2200
**   ~~~   **                                    Wair,out = 6.585921E-003
**   ~~~   ** The revised design conditions are: Tair,out = 9.2195
**   ~~~   **                                    Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL
**   ~~~   ** no apparatus dew-point can be found for the initial entering and leaving conditions;
**   ~~~   ** the coil outlet design conditions will be changed to correct the problem.
**   ~~~   ** The initial design conditions are: Tair,in = 25.9845
**   ~~~   **                                    Wair,in = 1.167724E-002
**   ~~~   **                                    Twater,in = 7.2200
**   ~~~   **                                    Tair,out = 9.2200
**   ~~~   **                                    Wair,out = 6.585921E-003
**   ~~~   ** The revised design conditions are: Tair,out = 9.2195
**   ~~~   **                                    Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 1
**   ~~~   ** the apparatus dew-point is below the coil design inlet water temperature;
**   ~~~   ** the coil outlet design conditions will be changed to correct the problem.
**   ~~~   ** The initial design conditions are: Tair,in = 25.9901
**   ~~~   **                                    Wair,in = 9.862493E-003
**   ~~~   **                                    Twater,in = 7.2200
**   ~~~   **                                    Tair,out = 9.2200
**   ~~~   **                                    Wair,out = 6.585921E-003
**   ~~~   ** The revised design conditions are: Tair,out = 9.2195
**   ~~~   **                                    Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 3
**   ~~~   ** the apparatus dew-point is below the coil design inlet water temperature;
**   ~~~   ** the coil outlet design conditions will be changed to correct the problem.
**   ~~~   ** The initial design conditions are: Tair,in = 25.9832
**   ~~~   **                                    Wair,in = 9.506870E-003
**   ~~~   **                                    Twater,in = 7.2200
**   ~~~   **                                    Tair,out = 9.2200
**   ~~~   **                                    Wair,out = 6.585921E-003
**   ~~~   ** The revised design conditions are: Tair,out = 9.2195
**   ~~~   **                                    Wair,out = 6.586107E-003
** Warning ** Controller:MechanicalVentilation = "CONTROLLER MECHANICAL VENTILATION 2", Zone="THERMAL ZONE5-1".
**   ~~~   ** No "PEOPLE" object has been specified in the ...
(more)
edit retag flag offensive close merge delete

Comments

Elena Guidolin's avatar Elena Guidolin  ( 2015-07-22 05:17:15 -0600 )edit

@Elena Guidolin please use existing tags whenever possible - e.g. "energyplus" not "energy+". Also, are you using OpenStudio? If not, please remove that tag. Thanks for helping to keep the site organized.

MatthewSteen's avatar MatthewSteen  ( 2015-07-22 08:08:53 -0600 )edit

sorry for the "energy+" tag..it has been an oversight..how can I change it? And yes I'm using Openstudio for this project. Thank u for the support.

Elena Guidolin's avatar Elena Guidolin  ( 2015-07-22 08:46:17 -0600 )edit

You can edit your question to change the tags or provide updates or additional information.

MatthewSteen's avatar MatthewSteen  ( 2015-07-22 09:02:09 -0600 )edit

There is also a 'retag' if you only want to modify the tags.

__AmirRoth__'s avatar __AmirRoth__  ( 2015-07-22 09:33:29 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2015-07-30 21:35:02 -0600

I'm shooting from the hip here, but try switching over to "DetailedAnalysis".

image description

edit flag offensive delete link more

Comments

thank you for the help, changing the option now i see this severe error FindRootSimpleController: Controller error for controller = "CONTROLLER HEAT COIL HWHTG" * Environment=RUN PERIOD 1, at Simulation time=09/19 18:06 - 18:07 * Controller function is inconsistent with user specified controller action = Normal action * Actuator will be set to maximum action * Controller control type=Temperature * Controller temperature setpoint = 22.32 [C] * Controller sensed temperature = 22.24 [C] * Controller actuator mass flow rate set to 8.32E-002 [kg/s] * Controller actuator temperature..

Elena Guidolin's avatar Elena Guidolin  ( 2015-08-05 08:51:01 -0600 )edit

Have you ever seen this error? What could it be?

Elena Guidolin's avatar Elena Guidolin  ( 2015-08-05 08:51:54 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer