Trouble with the HVAC setting
Dear all,
I am simulation a building using Openstudio and E+. The HVAC system is composted by a multifunctional heat pump (it makes simultaneously heating and cooling), a ground water condenser and cooled beams as air terminals that provided both the cooling and the heating in the zones. I have used the CentralHeatPumpSystem to simulate the multifunctional heat pump. I have used the PlantComponent:TemperatureSource to simulate the ground water used as condenser I have used the FourPipeInduction Air terminals to simulate the cooled beams. I can't understand why the simulation doesn't work properly and I have problems with the sizing of the objects and the convergence of the temperature.
Has someone of you any idea how should I do to solve this issue? I attach the idf below.
Thank you very much
Have a nice day
Elena
part of the error message:
************* Beginning System Sizing Calculations
************* Beginning Plant Sizing Calculations
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 2
** ~~~ ** the apparatus dew-point is below the coil design inlet water temperature;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 25.9833
** ~~~ ** Wair,in = 9.554298E-003
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 9.2200
** ~~~ ** Wair,out = 6.585921E-003
** ~~~ ** The revised design conditions are: Tair,out = 9.2195
** ~~~ ** Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL
** ~~~ ** no apparatus dew-point can be found for the initial entering and leaving conditions;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 25.9845
** ~~~ ** Wair,in = 1.167724E-002
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 9.2200
** ~~~ ** Wair,out = 6.585921E-003
** ~~~ ** The revised design conditions are: Tair,out = 9.2195
** ~~~ ** Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 1
** ~~~ ** the apparatus dew-point is below the coil design inlet water temperature;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 25.9901
** ~~~ ** Wair,in = 9.862493E-003
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 9.2200
** ~~~ ** Wair,out = 6.585921E-003
** ~~~ ** The revised design conditions are: Tair,out = 9.2195
** ~~~ ** Wair,out = 6.586107E-003
** Warning ** In calculating the design coil UA for Coil:Cooling:Water HW CHW FOUR PIPE INDUCTION TERMINAL CHW CLG COIL 3
** ~~~ ** the apparatus dew-point is below the coil design inlet water temperature;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 25.9832
** ~~~ ** Wair,in = 9.506870E-003
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 9.2200
** ~~~ ** Wair,out = 6.585921E-003
** ~~~ ** The revised design conditions are: Tair,out = 9.2195
** ~~~ ** Wair,out = 6.586107E-003
** Warning ** Controller:MechanicalVentilation = "CONTROLLER MECHANICAL VENTILATION 2", Zone="THERMAL ZONE5-1".
** ~~~ ** No "PEOPLE" object has been specified in the ...
my idf file
@Elena Guidolin please use existing tags whenever possible - e.g. "energyplus" not "energy+". Also, are you using OpenStudio? If not, please remove that tag. Thanks for helping to keep the site organized.
sorry for the "energy+" tag..it has been an oversight..how can I change it? And yes I'm using Openstudio for this project. Thank u for the support.
You can
edit
your question to change the tags or provide updates or additional information.There is also a 'retag' if you only want to modify the tags.