Rejecting condenser heat to a Districtcooling loop

asked 2015-07-13 14:28:26 -0600

kbk78's avatar

updated 2015-07-13 19:41:09 -0600

Hello, I am trying the setup a heatexchanger to reject condenser heat from a chiller to the districtcooling loop via a HeatExchanger:FluidToFluid Object. I tried to follow some details from "PlateHeatExchanger.idf file replacing the Ground loop with a District Cooling object. However I Get a error that the LOOP Demand side are not on the demand side of a plant loop and That the Heatexchanger was not found in any plant loop even though it is defined in the plantEquipmentList.

Is it possible to have such arrangement in Energyplus 8.1, thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2015-07-15 11:05:35 -0600

Archmage's avatar

Yes, this arrangement is possible. It sounds like the heat exchanger is not connected quite right. I would suggest studying the example file called PlantLoopChainCooling.idf.