How to model and size ASHP and GSHP HVAC system in DesignBuilder?

asked 2023-04-24 20:40:23 -0600

Kostas774's avatar

updated 2023-04-25 10:58:51 -0600

Hello,

I am currently working on a project of 5 floors, total conditioned area of 10 000 m2. DesignBuilder provides systems for Ground Source Heat Pump (GSHP) and Air Source Heat Pump (ASHP), but I have some problems finding the best way to compare these two systems, as well as connecting a DHW loop to the system. the indoor unit is probably going to be a FCU. My objective is to compare these two systems, but I have some questions about the systems. Since the project is in Athens, Greece, these systems should take care of the cooling, heating and Domestic Hot water demands.

For the ASHP for example, I find only a template for Heating only, and when I use it I have a lot of unmet hours, so I don't know how to size it correctly. What should I do for the Cooling Demand? Add a Air cooled Chiller? And how can I size the ASHP so the system can meet the heating & cooling load as well as the DHW load?

As for the GSHP, I don't really know how to size correctly the GSHP as it has very low consumption for such a big building.

Thank you for your support,

Konstantinos Dikaros

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-04-30 20:10:37 -0600

Greg Estep's avatar

Hello Konstantinos, Please confirm that you want to model zone level terminal units and not central ASHPs and central GSHPs.
Assuming that you want to model zone level equipment and vertical, closed loop ground heat exchanger, here is my advice:

In DesignBuilder, there are two ways to model ASHPs: (1) using PTHP. This simulates "mini-split" systems, where a single fan coil unit is connected to an outdoor, air source condensing unit. This object conditions a single zone. You can add this object from the HVAC zone level of detailed HVAC. (2) using air-source VRF. This object allows you to connect multiple indoor VRF units to a single outdoor VRF unit. You add the indoor unit the same way you would the PTHP. From the HVAC zone level, go to the "forced air unit" icon and select the indoor VRF. For the outdoor unit, you add this from the "add loop" icon. The outdoor VRF object dialog has the open to select the condenser type: water-cooled or air-cooled.

For the GSHP: (1) zone indoor unit: from the HVAC zone level, click the "add forced air unit" icon and select zone water to air heat pump. This object can be connect to the ground heat exchanger plant loop. (2) Ground heat exchanger plant loop: to add a ground heat exchanger (GHX), you will need to add a condenser loop and swap out the cooling tower for a GHX. I size GHX using a different software, called GroundLoopDesign (GLD). This will provide a much more accurate representation of the intended borefield thermal response. This program calculates and exports a G-Function for import back into DesignBuilder. However, for just getting started, DesignBuilder does offer some default GHXs in the component dialog.
(3) Be sure to use the DesignBuilder help website for setting this up.

For ventilation: what are you doing for ventilation air? We typically specify central ERVs with heat recovery (energy recovery) devices. you can add outdoor air direct to the zone level units, but that is typically not done and would require many exterior penetrations.

DHW: you will need to add the DHW loop from the HVAC system level. Use the Design Builder help. If you want to use an ASHP for DHW, you can find that from the "load HVAC template" dialog, or you can add the "heat pump water heater" from the DHW loop supply side level. The ASHP DHW can be added from the HVAC zone level, meaning that the unit is inside a zone and sourcing heat from that zone.

Things to keep in mind: for the ASHP: remember that capacity is degraded as temperatures get cold and there are low temperature cut offs. However, in Athens, I doubt this will be much of an issue. Also remember, that you will need multiple VRF outdoor systems to condition all 10,000 m2 of space. We usually, don't specify outdoor units much larger than 20 tons due to refrigerant distribution issues. The outdoor units offer "heat recovery" option ... (more)

edit flag offensive delete link more

Comments

Dear Aaron,

Thank you for your answer, I appreciate a lot. However I do think that I'm trying to model a central GSHP and ASHP system with a terminal four pipe (FCU) and an AHU connected to the central GSHP and ASHP system in order ro bring fresh air.

As for the DHW, is there a way to connect the DHW loop to the GSHP or ASHP loop in order to compare what consumption does it produce?

Thank you a lot for your assistance,

Konstantinos

Kostas774's avatar Kostas774  ( 2023-05-01 21:01:17 -0600 )edit

Hi Konstantinos, OK. In DesignBuilder, you can easily add water-to-water heat pumps right from the HVAC System level via the "add loop" icon. i.e. "add heat pump heating plant loop" and "add heat pump cooling plant loop". These objects can be connected to a condenser loop, which you can use a GHX. You can add air-to-water central heat pumps by following the steps above, then changing the heat pump "type field to 2-Plant Loop EIR heat pump" and then changing the "condenser type field to 1-Air source".

Greg Estep's avatar Greg Estep  ( 2023-05-02 10:46:11 -0600 )edit

You can connect the DHW to the heat pump heating loop by adding the DHW loop and changing the water heater type to "indirect" then connect the two loops.

Greg Estep's avatar Greg Estep  ( 2023-05-02 10:46:40 -0600 )edit