How to Record Damper Position

asked 2015-07-10 13:17:10 -0600

DW's avatar

updated 2015-07-10 13:24:55 -0600

Does anyone know of a way to record the damper position of an air-handling unit in OpenStudio or EnergyPlus?

When I look in the *.rdd file, I don't see anything that records damper position for a building's AHU (only zone VAVs).

I've set minimum and maximum values on my economizer trying to fix the damper in a particular position, but it doesn't seem to affect my minimum or maximum OSA %.

Any advice or ideas would be appreciated.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2015-07-10 22:24:57 -0600

Ivan Korolija's avatar

You might find useful the following output. For a detailed model evaluation it is worth changing the output frequency from 'hourly' to 'timestep'.

Output:Variable,*,Air System Outdoor Air Flow Fraction,Hourly;
edit flag offensive delete link more

Comments

Thank you, I've been using that output. This output does show the value that I use for the economizer minimum position. However, the flow fraction ends up going much higher than the maximum value I set. For example:

Econo Min = 0.75, !- Min Fraction of Outdoor Air Schedule Name Econo Max = 0.76, !- Max Fraction of Outdoor Air Schedule Name

When I track the OA Flow fraction, it's minimum shows at 0.75, but it's maximum shows 0.94. Does this mean that my damper is going open to 94%, and if so, how can I limit my maximum damper position?

DW's avatar DW  ( 2015-07-13 10:09:45 -0600 )edit

Can you check what you specified in the "!- Minimum Limit Type" filed. If you set it to "Fixed Minimum" than it will always provide at least the minimum airflow rate. In the winter operation this leads to the OA dumper position close to the fully open (sometimes 100% open as well). However, if you change it to "ProportionalMinimum" you should always have the OA flow fraction between specified values. This operation can have implication on indoor air quality since the OA flow can be significantly reduced, particularly during heating season.

Ivan Korolija's avatar Ivan Korolija  ( 2015-07-13 11:24:20 -0600 )edit

I have been using ProportinalMinimum for the "!- Minimum Limit Type", but I am still seeing OA Flow Fractions much higher than 0.76. Is there something else that is taking priority over the maximum limit I am setting?

DW's avatar DW  ( 2015-07-13 12:28:37 -0600 )edit
1

Discovered the problem: my Controller:MechanicalVentilation was what was requiring so much fresh air that it was over-writing the economizer max damper position that I had set. I guess it's a good thing because OpenStudio was preventing me from compromising IAQ until I specifically told it to, by removing that ventilation controller. Thank you for your help Ivan.

DW's avatar DW  ( 2015-07-13 12:51:07 -0600 )edit