Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

BEOpt MF errors vented-attic

asked 2023-04-10 13:23:35 -0600

muhl's avatar

updated 2023-04-19 09:18:06 -0600

Energy Model recently failed due to errors with attic-vented requiring a floor space. Model here.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2023-04-19 11:02:51 -0600

updated 2023-04-19 13:12:36 -0600

@muhl Thanks. I will try to address some bugs and other interface oddities I found while working with your file.

That said, note that BEopt doesn't want you to draw the entire MF building -- just the MF unit of interest and any adjacent spaces that affect its heat transfer. See the help file and provided sample files for some examples. So, for example, you shouldn't draw the attic if the MF unit of interest has another MF unit completely above it. You also should never draw the entire slab/attic of the MF building, just draw the slab/attic adjacent to the unit and note where the slab/attic is adiabatic (i.e., adjacent to slab/attic from other MF units).

Here's an updated version of your project file that is how I would expect this MF unit to be described: Updated model

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-04-10 13:23:35 -0600

Seen: 95 times

Last updated: May 03 '23