Error - Space Space 167 is not associated with a thermalzone, it will not be translated.

asked 2023-04-07 18:01:50 -0600

updated 2023-04-10 10:28:03 -0600

when exporting the old open studio file to IDF for energy plus simulation, I get the message that: Space Space 167 is not associated with a thermal zone; it will not be translated.

edit retag flag offensive close merge delete

Comments

1

@Shashwat.S is Space 167 assigned to a thermal zone in the OSM that you're trying to export to an IDF?

Aaron Boranian's avatar Aaron Boranian  ( 2023-04-10 10:28:28 -0600 )edit

Thank you so much. It worked. However, there is another issue pooped up after that- Error: Sub Surface 4 This sub-surface is missing its base surface; it cannot be drawn. Do you have any suggestions?

Shashwat.S's avatar Shashwat.S  ( 2023-04-11 15:45:00 -0600 )edit

@Shashwat.S it sounds like Sub Surface 4 has an input field for base surface -- a Surface object type that represents a solid, opaque surface like a wall that the sub surface sits inside of -- which is currently blank and needs to be set to the name of a Surface object.

Aaron Boranian's avatar Aaron Boranian  ( 2023-04-12 10:38:14 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2023-04-11 07:13:00 -0600

Surfaces must be assigned to a Space. A Space should be assigned a ThermalZone; a ThermalZone should have 1 or more Spaces.