Issue conversion E+ prototype school models

asked 2023-04-03 11:56:43 -0500

xfang's avatar

updated 2023-04-04 08:49:36 -0500

Hi there, We are trying to convert an old 0.9 E+ prototype school (reference building model) to the latest version. And after the version conversion and some manual changes, the file gives interesting warnings that I just can't figure out what is going on. There's a warning that says controller:outdoorair doesn't have an outsideair system when it actually does have one. and all the nodes connections look good and the same as other systems. I've checked multiple times and still couldn't figure out what goes wrong with this file. it doesn't allow me to attach idf file to unmet hours. Let me know if you have experienced similar issues or if someone's willing to take a look at this model.

If you have successfully converted one file, let me know if it can be shared. Thanks ahead! Xia

edit retag flag offensive close merge delete

Comments

@xfang if attaching a file doesn't work, you can also upload files to Google Drive, Dropbox, etc. and share the URL here so that others can access the files.

Aaron Boranian's avatar Aaron Boranian  ( 2023-04-04 08:45:17 -0500 )edit

Did you use the IDF Version Updater tool, which transitions an IDF across multiple versions automatically, or the Transition Version feature of EP Launch for incremental IDF updates?

Aaron Boranian's avatar Aaron Boranian  ( 2023-04-04 08:49:26 -0500 )edit

I used EP Launch transition version tool. https://drive.google.com/file/d/1KgYb... Here's the file. Thanks Aaron!

xfang's avatar xfang  ( 2023-04-04 09:28:37 -0500 )edit

never mind. I should've used utilities in EP-Launch

xfang's avatar xfang  ( 2023-04-17 14:51:34 -0500 )edit