Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Why ZoneHVAC:Baseboard:RadiantConvective:Water has an air loop?

asked 2023-02-09 13:17:18 -0500

nagpalh's avatar

updated 2023-02-13 11:00:28 -0500

Hello all,

I want to simulate a simple single zone room with a single radiator unit with District Heating supplying the hot water to it. I want to use ZoneHVAC:Baseboard:RadiantConvective:Water. However, in the documentation I read that in addition to the hot water loop, there is an air loop with an air inlet and outlet node. I can not imagine it physically, how a radiator unit has an air loop. Has anyone simulated similar system before?

Thanks in advance.

edit retag flag offensive close merge delete

Comments

1

(original comment now posted as an answer).

Denis Bourgeois's avatar Denis Bourgeois  ( 2023-02-09 15:05:48 -0500 )edit

I agree with Denis, you should turn that comment into an answer.

Julien Marrec's avatar Julien Marrec  ( 2023-02-10 02:37:59 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2023-02-10 05:50:12 -0500

The baseboard object output (not input) variables do include air inlet and outlet temperatures in degC. I suspect the inlet is simply the zone air temperature, the outlet: air temperature coming out of the baseboard. But I see no mention of an optional/required air loop. Am I misunderstanding your question? ... an answer (as suggested by Julien), originally posted as a comment.

edit flag offensive delete link more

Comments

Or perhaps the baseboard's input field for inlet node name was confused for an air inlet node when it's actually for a water inlet node?

Or something was misleading from the Engineering Reference?

@nagpalh can you share a link to the EnergyPlus web docs where you read an air loop is needed for the baseboard?

Aaron Boranian's avatar Aaron Boranian  ( 2023-02-10 08:48:35 -0500 )edit

@Denis Bourgeois@aaron Yes, the object does not need an air loop to be defined. However, I was confused because of the output variables which report Baseboard Air Inlet Temperature, Baseboard Air OutletTemperature and also Baseboard Air Mass Flow Rate. I couldn't understand where does these variables come from?

nagpalh's avatar nagpalh  ( 2023-02-11 09:14:19 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2023-02-09 13:17:18 -0500

Seen: 151 times

Last updated: Feb 16 '23