Description of Chiller EIRFPLR in I/O Reference

asked 2023-01-22 10:37:28 -0600

Keigo's avatar

I customised chiller performance curves of Chiller:Electric:EIR based on manufacturer's technical data.

I think the description of Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name in I/O Reference is incorrect. I/O Reference says that "This curve is generated by dividing the operating electric input power by the available full-load capacity (do not divide by load) at the specific operating temperatures.", but I think the curve should be generated by dividing the operating electric input power by the rated electric input power.

image description

I think the description in Engineering Reference is correct. image description

Pleaese correct me if I'm wrong.

edit retag flag offensive close merge delete

Comments

The nature of EIR is power (W) / cooling capacity (W), so I'm confident that the I/O Reference is correct. You might check the definition of EIR to gain confidence about this.