About DOE's prototype models

asked 2023-01-22 03:33:05 -0500

Kagami's avatar

updated 2023-01-27 12:28:46 -0500

Does the DOE prototype model comply with the ASHRAE 90.1 Appendix G baseline?

In my opinion it is not compliant, is this correct?

I checked the ASHRAE90.1 2019 prototype model data for the mid-office (climate is Honolulu) and it is a System5 HVAC model.According to Table G3.1.1-3, climate is 1A, floor area is 50000 square feet, use is Office then System6 should be the baseline model, so I believe DOE's prototype model does not comply with the ASHRAE90.1 AppendixG baseline.

*System5 - Packaged VAV with reheat *System6 - Packaged VAV with PFP boxes

edit retag flag offensive close merge delete

Comments

@Kagami what tool are you using to edit or view the prototype (EnergyPlus, OpenStudio, etc.)? Where did you get the prototype file from (energycodes.gov website, etc.)?

Aaron Boranian's avatar Aaron Boranian  ( 2023-01-23 09:24:02 -0500 )edit

I use EnergyPlus (ver 22.1.0) and I get prototype model from https://www.energycodes.gov/prototype....

Kagami's avatar Kagami  ( 2023-01-27 08:12:59 -0500 )edit