CHW cooling coil Error
Hello!
I'm trying to setup an AirLoopHVAC according to figure
Heating coil is connected to Boiler loop, and Cooling coil (CHW) is connected to Chiller loop. The air loop has setpoint manager single loop with referenced thermal zone for control. Zone is to be kept at 25ºC maximum, for occupied periods.
When running sim on OS, I keep getting the same warning:
Warning * SizeWaterCoil: Coil="CHWCLGCOIL", Cooling Coil has leaving air temperature > entering water temperature. * ~~~ * Tair,out = 12.800 * ~~~ * Twater,in = 82.000 * ~~~ * ....coil leaving air temperature will be reset to: * ~~~ * Tair,out = 82.500*"
The schedule for cooling coil loop (chiller loop) is defined with water leaving chiller at 7ºC, so i find this a bit surreal. I've checked the coils connection nodes and they are differently numbered so a think this is not the problem.
Why do I keep getting the error/warnig above?
Thankyou
@Kastro, question tags are used to route questions to other users who are interested or experienced in certain topics. Users subscribe to tags by marking them interesting in the box on the right had ribbon. They can then set their personal settings to receive email when questions with these tags are asked. To make email routing work, you have to tag questions with tags that people are likely to subscribe to, and a good guide to these is the stream of tags on the right, e.g., 'openstudio', 'energyplus', 'hvac', 'vrf', etc. Happy tagging. Hope you are finding the site useful!